    Question Warm Air Lowboy operation seems odd to me..

    I was in a small greenhouse the other day that had a warm air lowboy oil fired furnace. When it fired up the oil burner lit and started warming the heat exchanger as I'm used to seeing in residential furnaces. After a short time the fan kicked on and started blowing heat down the duct - all good. But then what I found odd was the fan shut off but the burner kept running until the heat exchanger warmed back up, then the fan kicked back on again. This cycle continued for half an hour till the greenhouse was up to temp (55 F). I'm just used to seeing both the fan and the burner run till the t-stat no longer calls for heat. Is that lowboy hooked up wrong and running up against a high limit or something or is that possibly normal operation. The owner said all warm air furnaces run like that... I've never seen one do it.

    TIA

    Neo

  2. #2
    Join Date
    Aug 2012
    Location
    North Dakota
    Posts
    517
    it sounds like it is working ok the thing is a low indoor temp causing the fan switch to open
    the one caution to that is most or all mfgs. wont back the warranty unless a min. indoor temp is maintained I believe (60')
    because the flue gases will condense while still in the hx when running at a constant low indoor (r/a) temp.

  3. #3
    Join Date
    May 2008
    Posts
    7
    Ok, Thanks for the reply. It just seemed odd that the fan was shutting off. Interesting about the condensing flu gas. The owner said he has to replace the flu pipes every other year. I guess the condensed flu gas is pretty corrosive.
    Thanks again.

    Neo

  4. #4
    Join Date
    Aug 2012
    Location
    North Dakota
    Posts
    517
    ah yes it is
    carbonic acid is produced in combustion

  5. #5
    Join Date
    Aug 2012
    Location
    North Dakota
    Posts
    517
    I dont no your relationship though the hx should be tested asap

  6. #6
    Join Date
    Sep 2002
    Location
    Northeast Ohio
    Posts
    4,841
    Opertion is normal. That fan control is operating by temperature, not a timed cycle. The return air is cool enough to cause the on off cycling you observed. As far as the chimney and flue pipe. Corrosion is very common in greenhouse environments and we see it around here all the time. Greenhouse oil furnaces are some of the nastiest oil units I work on.
    A good HVAC tech knows how, an educated HVAC tech knows why!

    DEM


  7. #7
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    1,962
    No matter the installation, the air flow across the furnace should be adjusted to maintain a minimum temperature rise across the furnace. Not that it would protect the furnace as hoped 100% by the manufacturer, but it would definately help the whole situation.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  8. #8
    Join Date
    May 2008
    Posts
    7
    Quote Originally Posted by firecontrol View Post
    No matter the installation, the air flow across the furnace should be adjusted to maintain a minimum temperature rise across the furnace. Not that it would protect the furnace as hoped 100% by the manufacturer, but it would definately help the whole situation.
    So, in other words the fan would be slowed down to reduce or stop the cycling and thereby keeping the heat exchanger hot and less likely to condense the flu gases?

  9. #9
    Join Date
    Sep 2002
    Location
    Northeast Ohio
    Posts
    4,841
    Quote Originally Posted by neosec View Post
    So, in other words the fan would be slowed down to reduce or stop the cycling and thereby keeping the heat exchanger hot and less likely to condense the flu gases?
    Under ideal conditions in a more controlled typical application. In this instance, my quess is there is no real duct system to speak of, maybe a plenum with possibly some ducting or possibly greenhouse poly tube air distribution, not return duct. Odds are, the air coming back to the furnace is considerably colder than the actual discharge air and irregardless of what is done the condition will persist. Slowing the blower to a degree that will allow for constant operation will decrease the airflow to a point that the throw and diffusion will be ineffective.
    A good HVAC tech knows how, an educated HVAC tech knows why!

    DEM


  10. #10
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,591
    Quote Originally Posted by neosec View Post
    So, in other words the fan would be slowed down to reduce or stop the cycling and thereby keeping the heat exchanger hot and less likely to condense the flu gases?
    It may already be operating within factory temp rise spec. 55F return air heated up 55F is only 110, the fan limit may be set to shut the fan off when the air temp drops to 115 or 120F.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #11
    Join Date
    May 2000
    Location
    Rochester, NY, USA
    Posts
    14,156
    I think I would also ask if the Fan/limit switch as been replaced lately. If the F/L is the wrong insertion length your going to get erratic cycling

    OR

    If the F/L is very old, the bi-metalic strip (which makes the thing work) could be weak, that would also give erratic operation
    BEING AN ADULT

    is the dumbest thing I have ever done

  12. #12
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,591
    Quote Originally Posted by jmac00 View Post
    I think I would also ask if the Fan/limit switch as been replaced lately. If the F/L is the wrong insertion length your going to get erratic cycling

    OR

    If the F/L is very old, the bi-metalic strip (which makes the thing work) could be weak, that would also give erratic operation

    What he is describing is common for oil furnaces without a blower on timer, in a green house application. Its not really erratic operation when the return air is 55F or less.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  13. #13
    Join Date
    May 2000
    Location
    Rochester, NY, USA
    Posts
    14,156
    Quote Originally Posted by beenthere View Post
    What he is describing is common for oil furnaces without a blower on timer, in a green house application. Its not really erratic operation when the return air is 55F or less.
    sorry, I blew right pass the "oil furnace" and who keeps a greenhouse at 55 I thought greenhouses were suppose to be warm
    BEING AN ADULT

    is the dumbest thing I have ever done

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event