    When you are checking operation of the circuit you changed the compressors on, is the other circuit also running. You said before that the evaporators are one atop of the other. If you only have one circuit running, the air flow will tend to flow more through the dry coil than the wet coil that is cooling. This will lower the evaporator pressure.

  2. #15
    Join Date
    Jun 2004
    Location
    Olean, NY
    Posts
    1,445
    Is it a mcquay?

    Sent from my MZ601 using Tapatalk
    Guinness for strength

  3. #16
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    2,163
    Also, may need to calculate additional charge if you upgraded to new possibly larger LLF or SLFs.
    But definitely want to get some head pressure controls and if not already, crank-case heaters.

  4. #17
    Join Date
    Mar 2013
    Location
    Cincinnati, Ohio
    Posts
    17
    This is a York unit. The evaps are staggered (to balance flow I am guessing) - one is about 10 inches behind the other and a foot higher...like building an evaporator staircase if that helps at all...

    I've only run one stage at a time.

    That's a good point about the drier, the new one is much larger...perhaps 3 times the size of the old one. Thanks!