    Old Pepsi Machine Compressor

    I have and old 70s pepsi machine that the compressor tries to kick on every 30 seconds or so. I put a 3-1 start on it and it does the same thing... Could it be out of freon? Mark

  2. #2
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,282
    Post Likes
    Thread relocated to AOP

  3. #3
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,781
    Post Likes
    from here my guess would be no.
    never saw a soda machine with a pressure switch.
    probably compressor going bad.

  4. #4
    Join Date
    Jul 2003
    Location
    Orange County N.Y.
    Posts
    1,177
    Post Likes
    Quote Originally Posted by HOPPEL View Post
    I have and old 70s pepsi machine that the compressor tries to kick on every 30 seconds or so. I put a 3-1 start on it and it does the same thing... Could it be out of freon? Mark
    Generally that set of circumstances ends up being a locked up compressor. A cause of it locking up could be low refrigerant, or dirty coils, or no air flow etc. A compresssor replacement is most likely necessary.

    ...Ron