    Floor/radiant heat - boiler size question

    Hopefully this is posted in the correct area, please move if needed.

    I'm retro fitting my house with floor heat, wife insisted new kitchen, which I don't think is necessary, so I insisted on floor heat, which is necessary, if the kitchen comes out,

    I have opportunity to nab a good sized 660,000 btu/hr boiler used relatively cheap and it's only 7 years old. . My concern is, can it be a bday situation to have it a bit bigger then heat demand? Or can one go by the phrase, better to have it and not need it then to need it and not have it? Later I plan on heating garage and pool for summer, and a small hot tub for winter. My concern was quick cycles to keep water hot, but if that isn't a worry, then I apologize for the trivial question.



    Sent from my rooted HTC Supersonic using Tapatalk 2 Pro

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    That better be one monster sized house ya got before that thing won't be hideously oversized. At a guess, 14,000 sq ft or more, maybe a bit less if it heats a pool.

  3. #3
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    3,427
    Post Likes
    There is really nothing about using that size of boiler that is close to a good idea. That is unless your home is ..... 10,000 square foot and you're going to heat the entire thing with hot water.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  4. #4
    Join Date
    Aug 2012
    Posts
    60
    Post Likes
    Thread Starter
    Zones in kitchen, dining, something with garage, dhw, and pool /hot tub.

    I wasn't sure if short cycles from the unit being too large for a small heat demand would damage it. Valve/solenoids/secondary switching..

    Sent from my rooted HTC Supersonic using Tapatalk 2 Pro

  5. #5
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,384
    Post Likes
    To say this boiler would be oversized would be an understatement to the max. It's like this.....let's say you're driving to California from Boston......and you wanted to be efficient however you had to stop and turn the car off and restart it at every stoplight, warning light, crossroad, train tracks, shopping center...you get the drift. You'd be more efficient in a bicycle than a car and probably get there about as quick. Grossly oversized boiler connected to numerous zones will be the recipe for a horrible disaster. Both for comfort and your wallet. How about actually have a professional figure what you need and size it close to that?? Maybe the money you'll save will pay for the wife's kitchen....Advice from an old married man......let the wife have her kitchen. Hint....hint....or you may be in the hot tub alone!

  6. #6
    Join Date
    Aug 2012
    Posts
    60
    Post Likes
    Thread Starter
    I'd rather buy the boiler for $, cut my heating bill in half, or at least pay the same and enjoy it, and put up a 8000$ pole barn to make cash on the side instead of killing a kitchen I can already use, and trade her in for a pair of 20yo's and enjoy them in the hot tub.

    Sent from my rooted HTC Supersonic using Tapatalk 2 Pro
    Last edited by beenthere; 03-11-2013 at 05:10 PM. Reason: price

  7. #7
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    So are you saying your going to quadruple your boiler size and cut your bill in half lol, maybe I misread that. I did get the trade in for a couple of 20yr olds part loud and clear though ha ha!

  8. #8
    Join Date
    Aug 2012
    Posts
    60
    Post Likes
    Thread Starter
    Forced air to heat house, nothing else.

    Like to switch to a boiler, and heat nearly everything and then some.

    Sent from my rooted HTC Supersonic using Tapatalk 2 Pro

  9. #9
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    What kind of boiler, cast iron or modulating? It really won't matter because it will be oversized any way you slice it and will be something you regret until your finally tear it out. If your doing low temp floor tubing your better off with a condensing boiler that can modulate down to the lowest load, it will also be more efficient. I would strongly recommend you don't but it's ultimately your choice.

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Using that size boiler, it will cot you more to heat your house. Firing up 660,000 BTUs to heat a 10,000 BTU load is not cost effective.

  11. #11
    Join Date
    Nov 2001
    Location
    Seattle, WA
    Posts
    8,352
    Post Likes
    Buy the boiler for five bills and sell it for 10 bills. That's the only way your are going to come out ahead on this deal. BTW, most likely you will never be able to sell that used boiler with that kind of BTU rating.
    "The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
    - Alexis de Toqueville, 1835

  12. #12
    Join Date
    Feb 2004
    Location
    michigan
    Posts
    677
    Post Likes
    It's only a good buy because no one wants it. If it's cast iron, good luck moving it.
    I am the "Wally". All others are meer imitations of the original.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •