Results 1 to 7 of 7
    Jul 2011
    NEW YORK
    AHU Recommended Insulation
    Dear Sir,
    Commercial AHU inside an MER. Where would it be advantageous to have insulation on a air handler unit that has a supply and return fan that is located indoors. We have a new unit that doesn't have any insulation on the return/oa ductwork that is indoors?
    What is the preferred insulation recommendations and why?
    Thanks,
    Bob C.
    Jul 2003
    Orange County N.Y.
    Quote Originally Posted by CHAMBERS87 View Post
    Dear Sir,
    Thanks,
    Bob C.
    In my experience there is only what the engineer preferes. Some like the regular 1-1/2" or larger roll type soft fiberglass insulation, some like internally lined insulation, some like having you install duct board over the ducts, and I've even had to insulate with different types of styrofoam insulations. It seems to be more about cost and efficiency than about what is more effective. Engineers have the final say for the most part.
    ...Ron
    Roof Rat
    Jul 2011
    NEW YORK
    What we have is insulation wrap. What is the recommended ductwork to be insulated? The OA Ductwork to return, mixing area?
    Please advise?
    Thanks,
    Bob C.
    Jul 2011
    Croatia
    ductwork that carries air with state equal or very similar to design indoor air conditions is not insulated as there is no purpose to have insulation.
    there is number of occasions where carried air is not of the same state, like return air lines through unconditioned spaces, return that exhausts heat directly from lighting fixtures and similar.
    you would need to look through the whole layout of your return ductwork to be able to decide whether and/or where insulation is needed (or not).
    Jul 2011
    NEW YORK
    1-So the indoor air handler unit (inside MER) that uses econ outside air damper to lower the supply temp and mixes with the return in the mixing chambers does not need insulation on the outside of the duct?
    2-Also the unit that has an extra DX coil aft the preheat to precool the mixed air should have insulation?
    I was under the idea from the OA ductwork to the return mixing area due to heat loss/and/or heat gain, insulation wrap on interior is recommended as per ASHRAE?
    Is that correct?
    Jun 2010
    Philadelphia PA
    If it sweats then you NEED insulation. For energy considerations, probably more important to see if doors / panels fit to reduce air leakage
    Jul 2011
    Croatia
    Is that correct?
    1- this looks like free cooling at winter time, anyhow, outside temperature is not the same as indoor temperature, most of time, so you do need insulation as per previous post.
    2- Similar to point one, dx coil will seemingly lower temperature, and again you need insulation.