Thread: Carrier Infinity HP with zoning
-
03-08-2013, 06:10 PM #1
New Guest
- Join Date
- Mar 2013
- Posts
- 2
Carrier Infinity HP with zoning
No one seams to be able to answer this. Carrier 25VNA w/FE fan coil with infinity zoning. Im about to install this system and am wondering if the zone dampers modulate with the zoning system. It appears that the dampers operate in a N/O or N/C position. I was told that the dampers do modulate, but I don't see how. If they do, the static pressure would increase when it approaches set point temp; that would create more problems. If the static pressure increases do the other dampers modulate open to compensate the pressure increase ?
Do the carrier dampers modulate or not ?
If they do, or not, how does the system respond?
-
03-08-2013, 07:57 PM #2
They modulate. Control will slow blower as low as possible and/or keep dampers cracked to move enough air. Also, the control utilizes the calculated damper leakage to help manage excessive airflow.
Merry Christmas

-
03-09-2013, 11:18 AM #3
New Guest
- Join Date
- Mar 2013
- Posts
- 2
Thankyou,
This is the first time I have used this type of forum. This is very helpful. Thank you