    Quote Originally Posted by danjohnson View Post
    If you look at this and think about it, you could have the breaker closed, and the blade installed, and not trip the breaker until the contactor closed.
    The unit is isolated from ground due to the whip being car-flex. and the chance the lineset could be a feasible ground is questionable.
    Read post 22 it did not short with the contactor closed. Apparently the line set and coil were not grounded.

  2. #42
    Join Date
    Aug 2012
    Location
    NE wisconsin
    Posts
    488
    Post Likes
    Plastic pan and gromets on the lineset through the case and yeah, I could see the coil being isolated.

  3. #43
    Join Date
    Feb 2013
    Location
    north georiga
    Posts
    2,998
    Post Likes
    how about when someone replaces an existing 3-phase unit with a new 3-phase unit and installs a single phase disconnect and wire nut the third leg together, 208volt service and it was the hi leg that they wire nut-ed. now that one hurt !!!

  4. #44
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Quote Originally Posted by davidj001 View Post
    how about when someone replaces an existing 3-phase unit with a new 3-phase unit and installs a single phase disconnect and wire nut the third leg together, 208volt service and it was the hi leg that they wire nut-ed. now that one hurt !!!

  5. #45
    Join Date
    Nov 2008
    Location
    DFW,TX
    Posts
    4,599
    Post Likes
    wow thats why we should never believe a disconnect works and check with meter before grabbing.

    that usually kills a compressor, causes short to ground..

  6. #46
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,115
    Post Likes
    I remember finding a 20kW air handler running direct off the lugs on the panel box, 200 A main was the only protection.

    I also remember getting bit off the 24v on a contactor I was changing, disconnect pulled. Checked and had 144v one side of the coil to ground. Tracedit back to a fan limit control that had been replaced but they never removed the jumper for the low voltage limit. Still don't know how it didnt' burn up the trans. or trip a breaker.

  7. #47
    Join Date
    Jun 2011
    Location
    Detroit vicinity, Michigan
    Posts
    79
    Post Likes
    If you don't check power/try to start equipment after throwing the disconnect, You're gonna have a bad time....M'Kay?

  8. #48
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    8,146
    Post Likes
    Ok update. I am going to put my klien away and go back to the greenlee volt stick.
    Although the klien seems to be more reliable, my OLD ears can't hear it as well as the
    Greenlee.

  9. #49
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes
    Quote Originally Posted by philjafo View Post
    That's for an anti theft feature.
    X2
    "If you've eliminated all other possibilities whatever remains must be the truth."

  10. #50
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    I recently bought a Milwaukee voltage detector on account of this thread. I dont trust it. It wont show potential across a light switch for some reason.

  11. #51
    Join Date
    May 2010
    Location
    Brooklyn, NY
    Posts
    99
    Post Likes
    correct me if i am wrong, but if the disconnect is inserted, then it will automatically trip the breaker since the White wire is grounded at the unit. Assuming there's not flame spot around the grounded white terminal, the circuit was never live for once.

  12. #52
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Quote Originally Posted by EEAllen View Post
    correct me if i am wrong, but if the disconnect is inserted, then it will automatically trip the breaker since the White wire is grounded at the unit. Assuming there's not flame spot around the grounded white terminal, the circuit was never live for once.
    The fault circuit is being used as a neutral, the chassis that is connected to the hot wire has no path back to the breaker box untill some unlucky individual provides one.

  13. #53
    Join Date
    Feb 2012
    Location
    central Florida
    Posts
    154
    Post Likes
    it is easy to be complacent when it's late and your tired from a long day or haven't had an accident for a while.

  14. #54
    Join Date
    Jan 2008
    Location
    Cape Cod, Massachusetts
    Posts
    19
    Post Likes
    Unbelievable!!

  15. #55
    Join Date
    Jun 2011
    Posts
    463
    Post Likes
    Great way to catch a copper thief. Bad way to kill a service tech.

  16. #56
    Join Date
    Apr 2013
    Posts
    10
    Post Likes
    One of the many hazards! !! Check this out...saw yesterday in a McDonald's rtu...Name:  uploadfromtaptalk1365048858537.jpg
Views: 394
Size:  48.7 KB

    Sent from my SCH-I535 using Tapatalk 2

  17. #57
    Join Date
    Jun 2006
    Location
    SW MO.
    Posts
    5,610
    Post Likes
    Thread Starter
    Quote Originally Posted by tech who shares View Post
    One of the many hazards! !! Check this out...saw yesterday in a McDonald's rtu...Name:  uploadfromtaptalk1365048858537.jpg
Views: 394
Size:  48.7 KB

    Sent from my SCH-I535 using Tapatalk 2
    Is there a meter to check for that?

  18. #58
    Join Date
    Jun 2011
    Posts
    463
    Post Likes
    All you have to do is energize the chassis and hope it kills the bugs...the big ones are normally grounded anyways.

  19. #59
    Join Date
    Aug 2012
    Location
    Antelope,Ca
    Posts
    93
    Post Likes
    I hate spiders!!!!

  20. #60
    Join Date
    Apr 2013
    Posts
    10
    Post Likes
    If you will look at the board close in this pic you will see some micro capacitors burnt. ...this was yesterday, 38º outside. ..she was all cozy right against the transformer. ..worse part was when I looked away to send this to fellow tech, she disappeared! !!!! I was checking my clothes all evening! !!Name:  uploadfromtaptalk1365052156211.jpg
Views: 244
Size:  65.3 KBName:  uploadfromtaptalk1365052178425.jpg
Views: 257
Size:  71.6 KB

    Sent from my SCH-I535 using Tapatalk 2

+ Reply to Thread
Page 3 of 5 FirstFirst 12345 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •