Thread: paint thinner in purging air conditioning pipes

  1. #1
    Join Date
    Aug 2012
    Location
    Iraq
    Posts
    1,396
    Post Likes

    paint thinner in purging air conditioning pipes

    its possible to purge the ac unit pipes with paint thinner
    i use it to clean the evaporator of window type ac
    so it cleaned it from oils and other contaminant
    so what advantage and disadvantage

  2. #2
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    There are many chemicals used as paint thinner, which specific chemical/product are you looking at?

    I wouldn't use anything marketed as a paint thinner for flushing the refrigerant cycle of an AC system.
    There could be components of it that will leave harmful residue in the system, and the moisture content may be unacceptable.

  3. #3
    Join Date
    Aug 2012
    Location
    Iraq
    Posts
    1,396
    Post Likes
    Thread Starter
    Quote Originally Posted by mark beiser View Post
    There are many chemicals used as paint thinner, which specific chemical/product are you looking at?

    I wouldn't use anything marketed as a paint thinner for flushing the refrigerant cycle of an AC system.
    There could be components of it that will leave harmful residue in the system, and the moisture content may be unacceptable.
    so what solvent you use to flush the ac system

  4. #4
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    unless the lines are contaminated from a burn out just blow them out with nitrogen

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    moved to tech to tech



  6. #6
    Join Date
    Dec 2005
    Posts
    94
    Post Likes
    Paint thinner sounds like a terrible idea. In the old days we used R-11 as a flushing solvent but that is no longer legal, and incredibly expensive if available at all. There is a product called RX-11 that can be used if you need something more than a nitrogen flush. Google RX-11 and it comes right up.

  7. #7
    Join Date
    Mar 2007
    Location
    Sterling Heights, MI
    Posts
    169
    Post Likes
    RX-11 is non-flammable but paint thinner is flammable. RX-11 is also approved for the use, while I would guess paint thinner is not, nor would it probably be compatable with system components. While you may not have this product readily available where you are, using paint thinner is probably not a good idea from a warranty point of view.
    Better Service Through Knowledge...
    RSES, The HVACR Training Authority. www.rses.org
    UWUA Local 223

  8. #8
    Join Date
    Aug 2012
    Location
    Iraq
    Posts
    1,396
    Post Likes
    Thread Starter
    Quote Originally Posted by catmanacman View Post
    unless the lines are contaminated from a burn out just blow them out with nitrogen
    thanx

  9. #9
    Join Date
    Aug 2012
    Location
    Iraq
    Posts
    1,396
    Post Likes
    Thread Starter
    Quote Originally Posted by tchntch View Post
    Paint thinner sounds like a terrible idea. In the old days we used R-11 as a flushing solvent but that is no longer legal, and incredibly expensive if available at all. There is a product called RX-11 that can be used if you need something more than a nitrogen flush. Google RX-11 and it comes right up.
    thanx
    some instruction about how to use it

  10. #10
    Join Date
    Aug 2012
    Location
    Iraq
    Posts
    1,396
    Post Likes
    Thread Starter
    Quote Originally Posted by rfhcms View Post
    using paint thinner is probably not a good idea from a warranty point of view.
    can you explain more

  11. #11
    Join Date
    Jun 2011
    Location
    New Braunfels, TX
    Posts
    116
    Post Likes
    I've heard of one AC company using Naptha as a solvent to clean the lines, but they had to be very careful to get the pure stuff because many brands have oils in them. I recently heard that they are using Coleman fuel on rag rolls shot thru the suction line with CO2 to wipe/clean the gunk out, then they do a final flush of RX-11,
    All this work to "save" on the RX-11 cost, but the labor goes thru the roof!

  12. #12
    Join Date
    Jul 2007
    Location
    Chicago IL
    Posts
    167
    Post Likes
    "Rag rolls"?
    I've never heard that. Sounds like a potential nightmare

  13. #13
    Join Date
    Jan 2013
    Location
    Henderson, NV
    Posts
    26
    Post Likes
    We had a rep from Lennox in the other day, and any trace elements of Rx-11 in an under warranty compressor will void the warranty.

    He said the engineers now say to use R-22 to flush linesets. Even on 410a systems.

  14. #14
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Quote Originally Posted by dwhitcomb View Post
    We had a rep from Lennox in the other day, and any trace elements of Rx-11 in an under warranty compressor will void the warranty.

    He said the engineers now say to use R-22 to flush linesets. Even on 410a systems.
    That rep must be who supplies you with R22 bc there's no way I'm wasting my R22 sweeping line sets, nitrogen is way cheaper.

  15. #15
    Join Date
    Feb 2013
    Location
    Summerville SC
    Posts
    117
    Post Likes
    like everyone else said I wouldn't use anything in a system that isn't for the intended use. get some type of flush kit. ive used most brands and pro-flush and rx-11 work well. after flushing into system you will want to purge the lines again with nitrogen to ensure you got all of whatever flush you used out. get a partner outside holding a rag over the lines as you purge them to make sure of whats coming out. if your still getting oil or flush keep holding the nitrogen to it

  16. #16
    Join Date
    Apr 2011
    Posts
    23
    Post Likes
    If I had to use anything other than RX-11, I think I would choose mineral spirits. Isn't mineral spirits a more pure solvent?

    However, mineral spirits is also very flammable.

    It would take a pretty good reason to using either thinnner or mineral spirits - maybe a really large system.

    Compressor manufacturers should indeed get pissed when a failed compressor comes back having failed because of system debris or RX-11.

    My understanding is that sometimes systems are really foul, but I have not had a lot of problems because of dirt in a system. It may have happened to that an very occasional capilliary tube has gotten plugged from dirt, but more often just restricted from baked in POE oil.

  17. #17
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    One guy I know uses denatured alcohol (from HD paint department). His theory is it totally evaporates and dries... I suggested to him it probably dries out before it washes away the junk in the lines.

    Personally... unless it is a burnout or green slime (that stuff is nasty), just blow it with N2. Better IMO to leave a little MO in the system... than to put something in the system that could cause damage.

    On the flush with R-22... Sounds like manufacturers trying to avid warranty responsibility. How many folks are gonna waste #'s of R-22 doing a flush. I do not know any of them.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  18. #18
    Join Date
    Feb 2013
    Location
    north georiga
    Posts
    2,998
    Post Likes
    i'd like to hear how you would keep the pressure and volume of r-22 high enough to clean the system AND not violate venting laws?

  19. #19
    Join Date
    Feb 2013
    Location
    Summerville SC
    Posts
    117
    Post Likes
    Quote Originally Posted by davidj001 View Post
    i'd like to hear how you would keep the pressure and volume of r-22 high enough to clean the system AND not violate venting laws?
    x2

  20. #20
    Join Date
    Oct 2002
    Location
    Lexington, NC
    Posts
    5,382
    Post Likes
    You guys that are just purging with nitrogen, what kind of pressure are you purging at? I have a lineset that I cannot remove and am up in the air as to what to do to clean it out. It started out that they wanted us to flush, then said don't flush because it can ruin the wiring insulation in the compressor, then said that up to 5% MO in the system is ok. So I really don't know what we are supposed to do. Whatever I do I am putting the line drier at the indoor unit to protect the txv, but there is one outside too so that is tit for tat.
    The main thing is to keep the main thing the main thing!

    Health = Wealth! To wager otherwise is a Fools Bargain

+ Reply to Thread
Page 1 of 5 12345 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •