  1. #79
    Join Date
    Feb 2004
    Location
    Pacific NW
    Posts
    558
    Since this thread opened again, will add in: (dont think I put this in last year)

    3 years ago, 'just for kicks' I built up an evaporator for a water source HP from used Cu pipe that had been open to the air for years, and used an old carrier finned tube HE out of the scrap pile for the condensor - which had also been open to the air for over 10 years.

    Incentive was the high price of copper.

    Filled the pipes and HE with a 10% solution of ferric chloride and let sit for 3 days, insides of pipe nice and shiny, with loose black Copper chloride suspended in the solution. Hooked up water hose to the setup and flushed for a few hours with well water.

    Pulled vacuum, let it run for a few days till <300 mirons held indication all water evaporated.

    Installed in system with all N2 precautions on silphos brazing, etc.. Has been running fine for 3 years, no problems.
    Lotta wait time involved, but little active time, not something you would want to have to travel to a job for on a customers old lines - and if you did, undoubtedly the vac pump would 'walk away' overnight? Probably not worth the time except to having seen if the proceedure works - have done similar for over 40 years with no failures I could track to the cleaning process. Have Never tried it on anything except pipe and tubing, pretty sure the technique would destroy a txv or compressor.

    BTW, have never put anything except refrigerent and the correct oil in any compressor.

  2. #80
    Join Date
    Oct 2002
    Location
    Lexington, NC
    Posts
    5,122
    I was reading an add for RX-11 Flush and it claims that it is non flamable. Diversitech brand also claims to be non flamable, so they must not have methanol in them.
    Quote Originally Posted by glennac View Post
    Good point. As I always blow to the outside and for what's it's worth Rx11 is also flammable and mostly methanol if not 100%. I also never have used air. Don't want to carry a air compressor along for the effort and I guess I never will. Thank you very much
    The main thing is to keep the main thing the main thing!

    If "the grass is greener on the other side", it likely has been fertilized with Bull$hit!

  3. #81
    Join Date
    Feb 2009
    Location
    Atlanta
    Posts
    99
    Both Pro-Flush and Rx11 are very flammable. The ingredients of each are also listed.

    http://www.us-ac.com/msds/Nu-Calgon%...RX11-FLUSH.pdf

    http://media.diversitech.com/doc/DOC27308.pdf
    “I walked a mile with pleasure, she chatted all the way. But left me none the wiser, for all she had to say. I walked a mile with sorrow and not a word said she. But oh the things I learned from her, when sorrow walked with me.” -Robert Browning Hamilton

    “For I reckon that the sufferings of this present time are not worthy to be compared with the glory which shall be revealed in us.” Romans 8:18

Page 7 of 7 FirstFirst 1234567

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event