    Working on a small walkin freezer that is about 1 1/2 yrs old. It has had the issue of moisture refreezing on the ceiling. Did have a backed up drain. That has been fixed. Otherwise freezer working ok. The defrost cycle does terminate aprox. 20 min. Looking for ideas to look at.
    Helgy
    Stupid is as stupid does. Don't be stupid!
    Dec 2011
    Northeast PA
    is it happing right in front of the coil?
    Minnesota
    freezer
    Yes it is. Seems like excess moisture off the evap.
    Helgy
    Dec 2008
    NW Iowa
    Clearing the drain will help rid excess moisture. Other things to look for are if the fans are not staying off after defrost until the coil refreezes. Also if you defrost too often, the water drops will vaporize instead of forming a drop and running down the coil and drain.
    Minnesota
    Good info. Heading back to the site tomorrow. I will run it through a complete defrost cycle. Thanks
    Dec 2006
    In a Mess
    what is defrost frequencey?
    how much is door opened?
    does door have strip curtains?
    Sig removed by mod. G-Rated site
    Jul 2012
    Western KY
    Typically a defrost termination issue, not terminating on temp and fans coming on while coil still warm. Force it into defrost with no ice on coil, should terminate pretty quick and fans should not start for a few minuts.
    Minnesota
    On site right now. I will try that. Thanks
    Minnesota
    What I came up with is the defrost term. Switch is working. I have 208v between 3 and X back at the clock. Still will not term defrost. Must have a bad defrost term relay in the time clock. Is this a common thing?
    Jul 2012
    Western KY
    Yep
    Southeastern Pa
    Quote Originally Posted by helgy View Post
    The failure I have found is the plastic yoke breaks in the back of the clock. It's toast.