Cant figure this out! Not getting 24v at the board or thermostat
Results 1 to 13 of 13
  1. #1
    Join Date
    Feb 2012
    Posts
    10

    Cant figure this out! Not getting 24v at the board or thermostat

    Its a Carrier split unit. Had the heater on yesterday and at some point when I wasnt around it turned off on its on. Its completely dead at the thermostat, and on the circuit board it doesnt get 24 volts either. So I tested voltage going into the transformer and it has 120 volts on all 3 wires going in but it only has .1 volts on the 24v side. Well thats not right. We have a 2 story house and both units have the exact same transformer so I measured the transformer on the working unit to be sure Im dong it right and it measures 120v on all 3 coming in, and about 27 volts going out. So I go and buy a new transformer, wire it up, and still no 24 volts! Did a resistance check, all wires have some resistance. So now Im stumped. If it has voltage coming in, how is it not coming out!? What should I check next?

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,336

  3. #3
    Join Date
    Feb 2012
    Posts
    10
    Quote Originally Posted by jpsmith1cm View Post
    The Yellow Pages would be a good choice.

    This isn't a DIY site
    Lol, I hear ya.

  4. #4
    Join Date
    Aug 2012
    Posts
    2,522
    Three wires going in? Your in over your head.
    Trying not to be a Hack.

  5. #5
    Join Date
    May 2008
    Location
    Central Fla.
    Posts
    311
    Quote Originally Posted by toocoolforschool View Post
    Three wires going in? Your in over your head.
    He is probably reading from leg to ground/neutral which would be 240 across the 2 hot legs.But not sure, he is in over his head though.

  6. #6
    Join Date
    Oct 2006
    Location
    The Beach
    Posts
    674
    For goss sakes call someone thats know what they are doing.
    Blue Fox

  7. #7
    Join Date
    May 2008
    Location
    Missouri
    Posts
    3,410
    We are forbidden to assist with DIY repairs! Call a pro. Sorry

  8. #8
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,604
    im wondering if the low volt fuse is bad ,also wondering what could have burned it out .a skilled service tech should be able to quickly find the problem and repair it
    We really need change now

  9. #9
    Join Date
    Feb 2012
    Posts
    10
    Winters coming here in n Florida and I finally tackled this problem again, on my own. And I fixed it too! Learned a good bit about the 240 Volts side, contactors, step down transformers. The problem turned out to be a solder point on the control/thermostat board that burned out/shorted out somehow. This solder point fed voltage to M1 (blower motor) and T3 (transformer) That's why I wasn't getting my 240 at the Transformer. Pics are here. I just bypassed the burned up point on the board completely -

    < Links to DIY sites are not permitted here. >
    Last edited by beenthere; 10-29-2013 at 05:38 AM. Reason: Removed link to DIY site

  10. #10
    Join Date
    Aug 2012
    Posts
    2,522
    So it took you five months to figure out that you had a faulty circuit board, Did you go to hvac school during that time you should have. Just to let you know it usually takes 30 seconds or so to check a board so your doing good. Why didn't you just pay someone to fix it, you know spread the wealth, keep the economy going support local business. not putting your life on the line Priceless. Geez you are cheap.
    Trying not to be a Hack.

  11. #11
    Join Date
    Aug 2012
    Posts
    2,522
    Oh and that website is a real winner, NOT> how foolish.
    Trying not to be a Hack.

  12. #12
    Join Date
    Feb 2012
    Posts
    10
    Quote Originally Posted by toocoolforschool View Post
    . Geez you are cheap.
    That's exactly why. One because Im cheap, and 2 because I love fixing things myself. I didn't work on it for 5 months straight lol. I have a 2 story house and this unit (downstairs) is only used during the winter. I quit working on it the first time (since winter was over) but your right, shouldn't have taken very long to fix. I actually wanted to go to HVAC school but I joined the military instead. They don't pay very good if you haven't heard. I didn't expect anything less from you guys on here as far as comments go lol.

  13. #13
    Join Date
    Aug 2012
    Posts
    2,522
    Quote Originally Posted by jayrod2 View Post
    That's exactly why. One because Im cheap, and 2 because I love fixing things myself. I didn't work on it for 5 months straight lol. I have a 2 story house and this unit (downstairs) is only used during the winter. I quit working on it the first time (since winter was over) but your right, shouldn't have taken very long to fix. I actually wanted to go to HVAC school but I joined the military instead. They don't pay very good if you haven't heard. I didn't expect anything less from you guys on here as far as comments go lol.
    Yea I did my time and learned a trade while I was at it, Navy- There are more ways too get paid besides monetary compensation, experience the paycheck that keeps giving.
    Trying not to be a Hack.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  