A loose rule of thumb... and we should NOT follow rules of thumb:
It takes around 3 times the watts to START an elec motor as it does to RUN the same motor. Whatever your run watts are (volts x amps)... then 3 times with some wiggle room probably will work.
I agree with Motoguy... a larger unit is a better choice. Remember that generally speaking: A generator will produce close to the same watts on LP gas as gasoline... yet around 20-25% LESS on NG.
Have a LICENSED electrician handle this for you.GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.
-
03-10-2013, 07:18 PM #15
Professional Member*
- Join Date
- Jun 2010
- Location
- Philadelphia PA
- Posts
- 2,139
How about a hard start kit to reduce LRA on start=up?