This thread isn't about an A/C system. It's a low temp R404A walk-in.
The only walk-in LT systems I ever see running at around 25ºF SH are the ones I've worked on.
Others often run at 50-60ºF SH or more.
Here's an old thread that might shed some light on what we're really talking about here. (Check out Basser's answer in post #35):
http://hvac-talk.com/vbb/showthread....ssor-superheat
-
03-06-2013, 08:41 PM #15
-
03-06-2013, 08:42 PM #16
-
03-06-2013, 08:43 PM #17
Professional Member
- Join Date
- Apr 2010
- Location
- San Diego, CA
- Posts
- 106
Don't know if its a Copeland, I was simply trying to point out that 25 superheat isn't high. I probably should have looked up the FAQ on the emerson website instead of throwing a number out there that has been rattling around in my head since my first Copeland class, because clearly I was incorrect. Copeland's minimum is actually 20. There is no maximum superheat, only maximum discharge temp. http://www.emersonclimate.com/en-US/...ompressor.aspxDo we know if this is a Copeland?
Now, it the manufacturer of THIS system says it should be 25, then fine. However, I don't think anyone in this thread, myself included, knows what the manufacturer wants to see for a sh value.
As Icemeister mentioned, there aren't many low temp systems out there running 25 or even 35° superheat at the compressor...
-
03-06-2013, 08:43 PM #18
Professional Member
- Join Date
- Apr 2010
- Location
- San Diego, CA
- Posts
- 106
-
03-06-2013, 09:00 PM #19[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
03-07-2013, 06:11 PM #20
You set superheat at the evap. If the lineset is short maintaining compressor superheat at 20* minimum is more important than evap superheat. I doubt that ambient would affect 2 ft of suction line that much. Learned it at copeland school actually. Regardless if I set it at 20 on a day that its 100 out I wont have any problems when its -20 out. Maybe that's why copeland says minimum 20 and not 5. Common sense.
-
03-07-2013, 07:24 PM #21
Meh. Not sure I buy this entirely.
A minimum superheat, from a manufacturer's point of view, is insurance for that compressor. With the proper superheat, a compressor can run for a VERY long time without giving the operator or the owner any problems at all.
It also ensures that the compressor will not see liquid under ANY circumstances. I don't see the heat added by ambient as a big factor in most equipment that I've ever seen. What I DO see as a factor, through, are system operating conditions.
Suction and head pressure fluctuations, liquid temperature fluctuations, frost loading on the evaporator, dirt loading on the evaporator, fan failure or possible multiple fan failures.
All of these things would affect superheat much more than the ambient temperature.
A TEV is designed and sized to be able to maintain a reasonably consistent superheat over the entire range of expected operating conditions, but we must remember that it is a mechanical device and is subject to limitations as such.
-
03-07-2013, 07:58 PM #22
Professional Member
- Join Date
- Mar 2013
- Location
- swan valley idaho
- Posts
- 106
hey guys, it is copeland, hermetic. I set to 25 sh at compressor because thats generally what is always recommended and is by koolpack who made this. still holding -10 fine, but checked today and superheat does fluctuate quite a bit. averaged 20 psi low side at -10 to -14 box temp. checked suction line at compressor periodically over a couple hours and it varied from -10 to 7 ?
drier only showed 2 degree temp rise inlet to outlet, sight glass clear except for a few seconds as fan cycles to it's lowest head pressure. cycle switch set to 200-275 psi
-
03-07-2013, 08:07 PM #23
Does this unit have a headmaster or an ORI/ORD valve setup?
-
03-07-2013, 09:32 PM #24
Professional Member
- Join Date
- Mar 2013
- Location
- swan valley idaho
- Posts
- 106
Just fan cycle. Head goes from 200-275 with cycle
Switch/fan
-
03-07-2013, 10:18 PM #25
Professional Member
- Join Date
- Apr 2010
- Location
- San Diego, CA
- Posts
- 106
Yeah, I probably should have worded my response there a bit better. I didn't mean to imply that ambient temp changes are THE reason for the minimum superheat number, just that the system is dynamic and conditions aren't going to be exactly the same from day to day, so the 20° superheat setting helps keep the pump from flooding when conditions worsen.
-