    CoAire Heat Pump - No outdoor fan
    Im trying to fix a heat pump. I may work on 1 or 2 a year so they are definitely my weakness. Anyway, its a CoAire model number COTH-48M2Z. I replaced the defrost control board after I found I have 24 volts input but did not have 24 volts output at the board. The low pressure and high pressure switches were both closed.
    With the new board installed the contactor now closes and the compressor comes on, but the fan does not. There is 120 volts going into the board at CN20 but no voltage coming out on the FAN terminal. If I bypass the board the fan comes on. Why is the 120 volts not leaving the new board? Thanks.
    http://imageshack.us/photo/my-images/803/photo1jjn.jpg/
    Eat a slice of Humble Pie.
    Virginia
    sounds like the defrost sensor is lying , and telling the board its time for defrost
    is the suction line getting hot when this occurs ?
    Feb 2011
    Georgia
    Kick it over in ac mode and see what happens
    Mar 2006
    DFW
    Could someone please give me the PDF file with the wiring schematic in this heat pump. I'm going to use your suggestions but wanted the schematic before I go back. Thanks
    Dec 2001
    St Louis, MO
    Feb 2013
    Florida
    Some boards you have to disconnect control voltage to momentarily and then go into a manual defrost to "learn" what a clean coil is
    Mar 2006
    DFW
    Thanks everyone. Tremendous help !!!