Never seen a sight glass on a unit with 10 degrees of subcooling...
How about one of those units that has a TEV and a sight glass but no receiver, or something like half of the units that have R507 in them?If it has a sight glass and a TEV and bubbles its wrong.
-
03-05-2013, 08:17 PM #15
Ryan - well yes .....did you mean ever see a unit with 10SC and bubbles?
-
03-05-2013, 08:34 PM #16
If you've got a head pressure control (I'm assuming here that you mean a headmaster valve) there is a specific procedure that one can follow to ensure proper charge.
http://www.parker.com/literature/Spo...90/90-30-1.pdf
It might seem a bit confusing, but it isn't really that tough to do.

Not often, but I have.
-
03-05-2013, 08:46 PM #17
Professional Member
- Join Date
- Jan 2009
- Location
- Salisbury, Maryland
- Posts
- 78
-
03-05-2013, 08:48 PM #18
I would suspect non-condensables or a pressure drop across the LLFD.
-
03-05-2013, 08:48 PM #19
-
03-06-2013, 06:18 AM #20
delete
Sig removed by mod. G-Rated site
-
03-12-2013, 08:21 PM #21
Professional Member
- Join Date
- Aug 2006
- Location
- Colorado
- Posts
- 236
Questions to Boss - True story
I made a cross country move and joined a large company. After many months probation pay and no raise and only working on rooftops, I moved to a small refrigeration company that really needed help. The price and benefits were right, so I signed on. I explained to them that I might be a little rusty from working on rooftops for a year, but I would get back to speed pretty quick. They said that would be okay. I gave notice to the big company and they fired me on the spot (standard policy) and started with the Refrigeration company. One day on the job I asked the service manager about what was the ideal temperature for an ice cream freezer (I really forgot). Exactly one week later I was fired and told that "we are not paying you a training wage". At least my co-workers told me that the manager was a little nuts and that I was the SEVENTH technician that he had done that to in the last two months.
Moral of the story is: Keep some phone numbers of technicians outside your company who you can talk to and ***** to and ask questions to. It makes the job much easier knowing you have someone to call in a pinch. The good thing is, thanks to that guy firing me, I found the best company, benefits, and wages that I have ever worked for.
-
03-12-2013, 09:06 PM #22
There is one exception to this rule that I know of. 414b See #4 and #5 under system charging http://www.icorinternational.com/images/hsss.pdf
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
03-13-2013, 09:26 AM #23
You can't correctly sub cool with a mixture of liquid and vapor, you must have a solid column of liquid all the way to the TXV.
Gas it up and let it shut down while you monitor system pressures, SH, SC, amp draw. Adjust from there if necessary.
-
03-13-2013, 09:31 AM #24
-
03-13-2013, 06:21 PM #25
-
03-13-2013, 07:12 PM #26
System charging
1. Initially charge 80% of R-12, 90% R-134a
and 100% of R-500. Do Not exceed
115% of OEM charge
2. Remove liquid only from cylinder
3. Charge refrigerant in the receiver or
high side of the system with the
compressor off.
4. Run system and add refrigerant if
needed to design subcooling. Adjust
TEV if needed. Never charge system by
clearing sight glass
5. For Fixed Metering Device Systems.
Charge by compressor superheatLocal 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD