    The use psychrometric air charts

    I am a student at HGTC and we had to give a presentation for class on the most important thing we learned.

    This is my video presentation.
    VIDEO

  2. #2
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Excellently done for a class of people who somewhat already understand relative humidity. Speaking strictly from a presentation standpoint, there are a few things you could have done to make that very well done presentation even better.

    Provide for a few "dramatic pauses" where your audience has time to think about what you have stated. Especially where you give calculations. Provide time for those in the audience who may not be following your calculationst to ask you to give them a way to better understand how you are getting to a calculated conclusion. Involve the audience a bit more.

    Be certain to give a brief definition of technical terms that may not be completely understood by all in the audience. Just because we understand the terminology we are using does not mean that all of those we are talking to do.

    You have a great capacity for memorizing data which allows you to be comfortable speaking without the constant use of notes. I would suggest joining a local Toastmaster's Club to hone the skills you already have. Toastmasters is a great way to try out new speaches on others while also working with a peer group that can evaluate your speaking in positive ways. Besides, the meetings are just fun.

    All in all, a good training speech.
    Training is important!
    Practical Training is a must!

  3. #3
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    The lesson was all wrong, but the presentation was very good. I'm not good at sugar coating, so that being said, I apologize for my brevity. Just understand that my comment is meant as constructive criticism. My impression is that you need further study on this subject.
    Last edited by hvacrmedic; 03-02-2013 at 08:11 PM.

  4. #4
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Hmmm, I have to admit that I was not really paying attention to the data. I was listening more from a speaker's point of view and not really paying attention to content. I'll have to relisten to understand what is wrong with the lesson. As I was doing other things while listening to the speaking structure, it sounded convincing enough.....

    Hvacrmedic, could you please comment on what was wrong with the lesson itself?
    Training is important!
    Practical Training is a must!

  5. #5
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by RoBoTeq View Post
    Hmmm, I have to admit that I was not really paying attention to the data. I was listening more from a speaker's point of view and not really paying attention to content. I'll have to relisten to understand what is wrong with the lesson. As I was doing other things while listening to the speaking structure, it sounded convincing enough.....

    Hvacrmedic, could you please comment on what was wrong with the lesson itself?
    Adding sensible heat to the air doesn't raise the dew point.

  6. #6
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Quote Originally Posted by hvacrmedic View Post
    Adding sensible heat to the air doesn't raise the dew point.
    That one piece of a comment, taken out of the context of the entire speech, does not seem to be what the speaker was implying. Are you discounting the entire lesson based on that one point?
    Training is important!
    Practical Training is a must!

  7. #7
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by RoBoTeq View Post
    That one piece of a comment, taken out of the context of the entire speech, does not seem to be what the speaker was implying. Are you discounting the entire lesson based on that one point?
    No, I'm discounting the lesson based on the long series of misstatements that followed that one.

  8. #8
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Quote Originally Posted by hvacrmedic View Post
    No, I'm discounting the lesson based on the long series of misstatements that followed that one.
    Are you taking into consideration the unusual circumstances of the moisture content in the floor? The dew point of all objects under such conditions constantly changes as the air is heated and cooled and as the concrete would be giving up it's moisture into the air.

    I'm just not understanding exactly what it is you are objecting to specifically. Can you let us know what exactly is wrong with the lesson and what would be the correct lesson learned? If the speaker is incorrect about why and how the moisture was being transferred from one medium to another and then how it was removed, can you tell us what really must have been going on?
    Training is important!
    Practical Training is a must!

  9. #9
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by RoBoTeq View Post
    Are you taking into consideration the unusual circumstances of the moisture content in the floor? The dew point of all objects under such conditions constantly changes as the air is heated and cooled and as the concrete would be giving up it's moisture into the air.

    I'm just not understanding exactly what it is you are objecting to specifically. Can you let us know what exactly is wrong with the lesson and what would be the correct lesson learned? If the speaker is incorrect about why and how the moisture was being transferred from one medium to another and then how it was removed, can you tell us what really must have been going on?
    First let's cover his stated theory, which was to wit, the moisture in the concrete was sucked into the room air by the air conditioners, making the air moisture laden, so that when the air was heated the moisture condensed out of the air into droplets, which then fell on the floor causing it to be wetted. That is just so wrong on every level.

    56° air at 50% RH is very dry air comparatively. It has a humidity ratio of 33.75 grains per lb (da). Raising that air to a temperature of 70°, without adding or removing moisture, or IOW still at 33.75 grains, would reduce the RH to 30.56%. The dew point would remain unchanged at 37.64°, well below floor temperature, which even with evaporative cooling could be no lower than about 47° (wb temp).

    So if condensation is forming on the floor, then moisture is being added to the air from some other source until its dew point is above the floor temperature. Well, if the moisture was being added to the air from the concrete floor, then it wouldn't be that same moisture collecting on the floor's surface. IOW, water cannot be evaporating and collecting simultaneously from/on the same surface. Thus the moisture had to be from infiltration and/or reevaporation from the evaporator coils. When you switch from cooling to heating mode with a short delay between modes, the moisture on the coil reevaporates, and will temporarily raise the humidity ratio and dew point in the space. This in itself could account for condensation on the floor's surface. Infiltration of wetter air could equally account for it.

  10. #10
    Join Date
    Aug 2011
    Location
    Myrtle Beach SC
    Posts
    97
    Post Likes
    Thread Starter
    I am not going to argue about this. It's easy to be critical and have all the answers when your not the tech on site. I will ,however, give you some more information.

    The original presentation was 1:18 I had to condense it down to :15. So some details that did not move towards the point, were cut out to make room.

    The concrete was unsealed. So there was a considerable amount of moisture in it,and I think we were only drying the very top of it. Allowing the moisture continue to permeate through the concrete.

    The idea the super had was to dry the floor and have it condense in the evaporator and exit threw the condensate line. So why did that not happen? Because the duct work became saturated on the supply side. I.E. re-evaporating.

    "Raising that air to a temperature of 70°" Remember we are heating only the air in the beginning. The air coming out of a 20KW bank is 120-140*F At that temperature with 2700CFM in a 1200SF space the "air's" dew point would change and cause it to "rain" in the space and accumulate (Not condensate) on the floor. "That part I did clarify at the end of the presentation." I left it open until the end to see who would catch it.

    Now. Before you go all crazy and tell me where I am wrong in all this. The point of the presentation and the purpose of the lesson was to show the importance of psychometrics and the use of charts. I was able to plot a heading on the chart and prove what I was saying would work. Satisfying the customer.

    Also:
    It worked. All the nonsensical arguing in the world, coupled with a litany of recorded information about the conditions of the space. Will never convince the critic. What I was experiencing in the space and what I did to solve it. Worked. So I used it in my presentation. I went over "ALL" the data with both of my instructors and they agreed.

  11. #11
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Thank you for sharing I enjoyed it.

  12. #12
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by Adamscarpentry View Post
    "Raising that air to a temperature of 70°" Remember we are heating only the air in the beginning. The air coming out of a 20KW bank is 120-140*F At that temperature with 2700CFM in a 1200SF space the "air's" dew point would change and cause it to "rain" in the space and accumulate (Not condensate) on the floor. "That part I did clarify at the end of the presentation." I left it open until the end to see who would catch it.
    The supply air at that temperature would have an initial RH in the vicinity of 3-5% leaving the supply, which can be plotted easily on a psychrometric chart. Find your initial state point, then move to the right along the horizontal dew point line to the new dry bulb temperature. Find the RH at the new state point. Even if your chart doesn't go as high as 120° db, you should be able to see that RH drops as you move to the right along the dew point line, and that since it is the dew point line, dew point doesn't change.

    Needless to say the sensible heating of the air in and of itself did not cause the fog. It just doesn't work that way. If OTOH the very dry supply air was impacting the floor, picking up moisture from the floor and leaving with a high RH while remaining higher than average room temp, then yes, a fog could result as that air further mixed and cooled to room temp. A portion(s) of the floor would have been acting as a humidifier pad. In this case the level of condensation across the floor would not have been uniform while the heat was running, since part of the floor would necessarily be giving up moisture in this process rather than accumulating it. A similar mechanism is at work in the heat pipe. This is also the possibility that Robo was alluding to in his earlier post, but apparently couldn't pin down. I didn't go into it because you seemed to indicate that the entire floor surface was being wetted by the fog while the heat was running. At shut down, yes, the warmed portion of the floor would cool due to conduction of heat to the underlying layers of concrete, and could also accumulate condensation after the fact. You will have basically redistributed the moisture from the interior of the concrete to its surface. Now if it was literally raining from the ceiling due to condensation there, then that would be yet another scenario.

    Regardless of the mechanism at work in that particular case, and I agree it was a good problem to base a lesson on. ?But the supposed purpose of the video was according to your own words a lesson in the practical use of the pscyhrometric chart. On that account, when I assume the role of a student, I can't say that I learned anything at all about the psychrometric chart from watching that video, except maybe what a psychrometric chart looks like. The definitions of the terms provided were for the most part incorrect, and the behavior of air under changing conditions was incorrectly described. It was a case of a correct solution based on faulty premises, and for that reason I have to say it fell short of its mark. Your presentation skills were however above average, and I commend you for that.
    Last edited by hvacrmedic; 03-03-2013 at 01:07 PM.

  13. #13
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Enjoying this conversation. Medics posts often need to be re read several times before I fully comprehend- But alsways very informing .

    I personally was trying to grasp the statements that the air expands In the video.

  14. #14
    Join Date
    Aug 2011
    Location
    Myrtle Beach SC
    Posts
    97
    Post Likes
    Thread Starter
    Medic was just waiting for my response so he could pounce. Probably already had the diagnostic typed up so he could just copy/ paste. Typical Heckler know it all.

    Sent from my LG-P999 using Tapatalk 2

  15. #15
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    I would have to agree with the OP on the statement that he was only drying the top layer of the concrete. Drawing moisture to the surface of solid concrete is a very slow process, the change of air temp. described here would not effect it much. Solid concrete takes around 20 years to full dry or "temper".

  16. #16
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by Adamscarpentry View Post
    Medic was just waiting for my response so he could pounce. Probably already had the diagnostic typed up so he could just copy/ paste. Typical Heckler know it all.

    Sent from my LG-P999 using Tapatalk 2
    I readily admit that I don't know everything. I'll even admit that I know virtually nothing about some aspects of this trade. This just doesn't happen to be one of those. I stated my intention right from the start. Take it or leave it.

  17. #17
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by Adamscarpentry View Post
    I am a student at HGTC and we had to give a presentation for class on the most important thing we learned.

    This is my video presentation.
    VIDEO
    This needs more discussion later!
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  18. #18
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,430
    Post Likes
    Quote Originally Posted by Adamscarpentry View Post
    Medic was just waiting for my response so he could pounce. Probably already had the diagnostic typed up so he could just copy/ paste. Typical Heckler know it all.

    Sent from my LG-P999 using Tapatalk 2
    Nope, not hvacrmedics style.

    Don't get all defensive and start running folks off that could give you some valuable information later on.

  19. #19
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by mason View Post
    Nope, not hvacrmedics style.

    Don't get all defensive and start running folks off that could give you some valuable information later on.
    Appreciate it mason, but I'm doing ok. Teddy Bear is on the scene, so I'm going to stand by eagerly awaiting his input. When Teddy Bear speaks I listen closely. I've learned a lot about moisture and humidity from his posts. I defer to his expertise on this one, and since he's a little softer in his approach maybe the OP will be more open to his input.

  20. #20
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,015
    Post Likes
    This is an important and confusing topic. If someone is going to explain it they should get it right so we can all understand it better. RH has always been a mystery to me. After reading this thread I googled RH and now have a little bit better understanding of RH.
    I think what was happening is that by heating the air, the saturated vapor pressure of the moisture in the air increased while partial pressure of the moisture in the air remained unchanged. Therefor the RH decreased because RH is the ratio of partial pressure of the moisture to the saturated pressure of the moisture. This should be a familiar concept for most of us because we deal with pressure temperature relationships all the time in the context of refrigerants in a closed system. If we increase the temperature of a saturated system then it's no longer at equilibrium and the refrigerant will evaporate until the pressure increases and re-establishes it's equilibrium. So, increasing the temperature of air increases the saturation pressure of the moisture and the RH decreases and liquid moisture evaporates to try and reach it's saturation equilibrium. So the heated air will absorb moisture initially but as it moves across the slab it will gradually cool and start to condense. Thus the "fog".
    I do like OP attempt to calculate the amount of grains of moisture he needed to remove and the amount of BTUs required. I'm not sure if he got it right because I think there might be a lot more variables involved but I do applaud his attempt.
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
    http://www.campbellmechanical.com

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •