    Quote Originally Posted by 22nomo View Post
    This sounds like a Berg chiller, they just have a cover over the chilled water tank that you can lift off and check the glycol level.
    It's a Schriber Chiller and it does have a cover that you lift off to access the evaporator and glycol. There is also a gauge glass to see the level.

  2. #15
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    997
    Quote Originally Posted by hands View Post
    This is an inside system, no dirt and the room is clean for a factory. There is also a cartridge filter in the loop. It looks clean other than the dark glycol solution. I have a new drum of glycol (30%) on site. I'm just waiting for them to give me a shutdown.
    i see, the water will get dirty looking and as long as there are no particles i guess your fine..Normal...but i would still get the water tested and analyzed to make sure you are controlling corrosion and bactria.

  3. #16
    Join Date
    Feb 2005
    Location
    Tampa Florida
    Posts
    784
    Hands, drain the system and fill with fresh water, add a product called Citranox for cleaning. I try to run the cleaner for 24hrs at a elevated temperature for the best results. After its clean pull the top and wash the tank out very good and drain several times. Try to get all the tap water out of the system, then use a 50/50 mix of distilled water and propylene inhibited glycol.
    Stay on top of the 50/50 mix and maintain.

    BTW, I use Protek 100 in all my open loop chillers.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event