    Programming and commissioning through FX-60

    Hey guys, is there a version of the commissioning software that would allow us to upload, download, commission, etc.. Unt's or Vav's through an FX front end? Also would this allow us to do so remotely with certain ports open?

    Thanks

  2. #2
    Join Date
    Dec 2012
    Posts
    49
    Are you asking about N2 Tunneling? I think it requires an upgrade to the license. Here is a good discussion about it... http://hvac-talk.com/vbb/showthread....0-n2-tunneling.

  3. #3
    Join Date
    Dec 2012
    Posts
    49
    Sorry, I forgot. HVAC Pro and GX 9100 are not supported. It is mentioned in the Workbench procedure.

  4. #4
    Join Date
    Oct 2009
    Posts
    572
    You can use the bacnet routing fuction if youre using the pcg controllers. It is also possible with the old legacy fx controllers too, bacnet and n2 both work. Its painful with the fx n2 controllers though.

  5. #5
    Join Date
    Jun 2007
    Posts
    148
    Sorry, I should have clarified. My intent was to reprogram or commission a UNT hanging on an FX60. I know with our NAE's it's possible with tools, just looking to do the same with the Jace. I did come across an older thread that mentions needing to disable the bus then tunnel through to upload and download. This thread is 5 years old though. Didn't know if anything has changed good or bad to support this?

  6. #6
    Join Date
    Dec 2012
    Posts
    49
    Code No. LIT-12011149
    Issued August 2, 2011
    Serial Tunnel and HVAC Pro Due to inconsistent behavior between HV AC Pro and the Serial Tunnel Service, HVAC Pro downloads are not supported. Serial Tunnel and GX 9100 Programming Tool
    Due to inconsistent behavior between GX 9100 Programming Tool and the Serial Tunnel Service, GX 9100 downloads are not supported.

  7. #7
    Join Date
    Jun 2007
    Posts
    148
    Got it. Thank you for the info.

    Has anyone found a third party work around to do the same?

  8. #8
    Join Date
    Oct 2009
    Posts
    572
    Unplug the N2 trunk from the FX60 and plug it into this http://s2innovations.com/s2usb485-interface now scan and upload with HVACpro. Kind of a pita but its the easiest thing to do.

  9. #9
    Join Date
    Feb 2005
    Location
    Edmonton, AB Canada
    Posts
    584
    Quote Originally Posted by kontrolthis View Post
    Got it. Thank you for the info.

    Has anyone found a third party work around to do the same?
    Good day KontrolThis,

    Stay tuned... We have something in the works for one of our customers. Sadly, it will be a few months before I will have additional info/results that I can post.

    Cheers,

    Sam

  10. #10
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    1,441
    s2sam,
    Now you have my attention !

    I really, Really, REALLY, want to know what you have in the works. Email me when you have something to share, Please !

    A driver ? An interface ? What ???? I know, it will be a few month but I don't want to wait.

    Thanks
    If sense were so common everyone would have it !

    All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!

  11. #11
    Join Date
    Feb 2005
    Location
    Edmonton, AB Canada
    Posts
    584
    Quote Originally Posted by Cagey57 View Post
    s2sam,
    Now you have my attention !

    I really, Really, REALLY, want to know what you have in the works. Email me when you have something to share, Please !

    A driver ? An interface ? What ???? I know, it will be a few month but I don't want to wait.

    Thanks
    Good day Cagey,

    Sadly, I cannot give you too many details just yet, as the project has not yet officially started (currently 3 ahead of this one). What I can say is that we have three different approaches that we will be evaluating/testing to see what works best... If all goes well, then the solution/variation would be applicable to non FX Users too. I will report back once I have more concrete information, but like I said, it will be a number of months yet.

    Cheers,

    Sam

  12. #12
    Join Date
    Mar 2007
    Posts
    361
    Quote Originally Posted by s2sam View Post
    Good day Cagey,

    Sadly, I cannot give you too many details just yet, as the project has not yet officially started (currently 3 ahead of this one). What I can say is that we have three different approaches that we will be evaluating/testing to see what works best... If all goes well, then the solution/variation would be applicable to non FX Users too. I will report back once I have more concrete information, but like I said, it will be a number of months yet.

    Cheers,

    Sam
    Let us know if you need beta testers.

  13. #13
    Join Date
    Jun 2007
    Posts
    148
    Yes likewise.

    Thanks

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event