    Recommendations for water in plenum

    Hi,
    Two nights ago we had quite a bit of rain/snow fall and in the evening my wife heard what sounded like dripping water coming from the air ducts. (These ducts are in the concrete slab). I pulled the couch back and sure enough I saw a water up to the edge of the bottom of the metal flashing. Through some other research and phone calls we had a camera inspection company come out to day and scope all the ducts. We found that they were in pretty healthy shape with no mold and only a few rust spots. There was definitely water in the plenum and the dirt/mud residue was throughout the ducts. It was recommended that a sump pump installed near the plenum would resolve the issue, but I am curious if that just fixes the symptoms of the water leaking in? Should we invest in proper french drainage-- having the ducts coated-- or just take them overhead?? Thanks in advance.

  2. #2
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,744
    the only 100% cure for this is an overhead duct system.
    a sump pump would remove most of the water but still leave the system damp, musty and a possible place for mold.
    a french drain MIGHT stop water from getting in but no way to know for sure.

    we have done a few that we converted to overhead system and just filled the old system with concrete to seal it off.

  3. #3
    Join Date
    Dec 2011
    Location
    Fort Worth, TX
    Posts
    80
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary, or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 02-28-2013 at 04:22 PM. Reason: Non Pro * Member

  4. #4
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    3,192
    if water is getting in, air is getting out. the ductwork is leaky. coating could be an option, but it would not address the water table issue you have to your slab. coating can reduce the likely already inadequate ductwork sizing and cause air distribution issues. overhead ducts means into the attic where heat gain will reduce your cooling capacity of your existing equipment...
    landscaping may be all that's required to divert the water runoff, heck, it could be as simple as changing your gutter downspout diverter...
    The TRUE highest cost system is the system not installed properly...
    The three big summer hearththrobs...
    Mel Gibson
    Dwane Johnson
    The A/C repairman

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event