    Staefa PC-Tool RJ11 to DB9 cable
    Anyone know the pinout? The only that I see floating around is RJ45. The smart 2s are RJ11.
    Feb 2013
    Central Pennsylvania
    I think you might have the right thing, it is actually an RJ-25, which is the same size as an RJ-11, but uses all six positions/conductors.
    RJ-45 is eight positions.
    show me the diagram, and I can ring my cable out?
    Mar 2011
    Galveston, Texas
    PCTOOL PIN OUT
    DB-9
    1
    2 BLACK
    3 RED
    4 WHITE JUMPER
    5 GREEN/YELLOW
    6 WHITE JUMPER
    7 RED JUMPER
    8 RED JUMPER
    9
    RJ-11 TAB FACE DOWN, IN FRONT, A-F
    A WHITE
    B BLACK
    C RED
    D GREEN
    E YELLOW
    F BLUE
    Feb 2013
    Virginia.
    Quote Originally Posted by Txwinger54 View Post
    PCTOOL PIN OUT
    DB-9
    1
    2 BLACK
    3 RED
    4 WHITE JUMPER
    5 GREEN/YELLOW
    6 WHITE JUMPER
    7 RED JUMPER
    8 RED JUMPER
    9
    A WHITE
    B BLACK
    C RED
    D GREEN
    E YELLOW
    F BLUE
    By red jumper and white jumper, does that mean 7 and 8 meet C on the RJ11?
    Mar 2011
    Galveston, Texas
    I found an old cable and it didn't have the two jumpers so try it without them.
    Essentially, RJ11 - B C D & E connect to DB9 - 2 3 & 5 respectively.
    Hope that helps,
    Rick