Results 1 to 13 of 13
Thread: What is this???
    Oct 2009
    Mukwonago, WI
    What is this???
    Plan called for economizer mixing boxes to be installed on the bottom of the furnace, with the return air coming out the side, and the OA coming out the back. This is what we got.
    • 5 ton systems, not sure what kind of mixing boxes these are, but they aren't right. oa choked down to 6/24 and return air choked to 8/24.
    • On two of the units, the mixing box is install on the OA duct, left side of furnace, the return is ducted into the right side of the furnace.
    • Why bother to glue the vent piping???
    • The OA intakes are supposed to be 16/20 with 1/2" mesh on the inlet, we get resi style inlet hoods. yup, that will work.
    The condensers arn't even wired (low voltage) and this contractor called the job done. There is also a 10 item punch list from the engineer. I found 8 more things he missed.
    How do these guys live with themselves
    Attached Thumbnails Attached Thumbnails Click image for larger version.
ID:	360961   Click image for larger version.
ID:	360971   Click image for larger version.
ID:	360931   Click image for larger version.
ID:	360941   Click image for larger version.
    Dec 2010
    With 5 ton systems the return needs to go into both sides, bottom or bottom/side combination. I did a bottom/side installation for my 3 ton system. It's just me!
    Oct 2009
    Mukwonago, WI
    yea, but there isn't return air ducted into both sides.
    Dec 2010
    Quote Originally Posted by Miller257 View Post
    It's hard to tell from the pictures. One furnace (on the right) for sure is incorrect. The other picture (of the other furnace) looks like there is a return "drop" on both sides.............but it's not clear.
    Oct 2005
    Indiana
    Also looks like the flue terminations are not factory approved.
    Jan 2013
    Champaign Illinois
    Looks like 10 lbs of s@&$ in a 5 lbs bag. I would have put furnaces on pedestal boxes to get side and bottom air flow. Guess you get what u pay for. Cheepest bid doesn't equal best work.
    Jul 2009
    Columbia, MD
    i dont believe there is any furnace (trane, carrier, lennox, rheem...) that you can get 2000cfm out of the side.
    it either needs to be both sides cut into, a side and a bottom or just the bottom
    Oct 2009
    Mukwonago, WI
    Quote Originally Posted by Jkb79 View Post
    They were supposed to be mounted on a mixing box with return out of the side and OA out of the back, guess he can't read plans either.
    Jan 2013
    Henry county,ky
    Residential hacks I swear. If you'll cant do any type of commercial, stay off the porch. Well, wait, never mind. Find a new career
    " dirty filter??!!! Buts its only 2 years old"
    Jun 2002
    south jersey
    Is this a strtup you were doing for the company you work for? Install guys work with your company?
    You need to put the phone down and get back to work!
    Float'N Vally, MS
    So this job was "designed" by the in jun ear?
    He sized the ductwork?
    Life is too short, Behappy!
    TFMM
    Oct 2009
    Mukwonago, WI
    haha it was a bid spec job, that the installing contractor decided to re-engineer.
    Float'N Vally, MS
    He would be in deep do do here.
    TFMM