Open Heating Element
Hey Capz, how's it goin'?
When you mentioned open heating element, do you mean an element that's in the on position or an element that's not working?
I'm not sure how you meant that. But your post seems really on the mark about the random humidity. I just went to a call like this.
I'm on my way back, never did a diagnostic on it yet. Too much other stuff in front of that.
Russ
-
03-05-2013, 09:13 AM #28
Professional Member
- Join Date
- Jul 2011
- Location
- Lehigh Valley, PA
- Posts
- 226
Open element=no resistance thus no current passing thru or possibly the element could be wired in series with a temp switch. I.e. closes at 25F opens at 45F. usually if an element opens it causes a short but I guess it's possible it doesn't short to ground & trip the breaker.
-
03-05-2013, 09:27 AM #29
-
03-05-2013, 10:10 AM #30
-
03-05-2013, 10:13 AM #31Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
03-05-2013, 10:31 AM #32
Was working on a wi freezer several yrs back where the pan was icing.
The drain was trapped and freezing (yes heat tape).
I called it in and was going to reduce it (trap was like 6"
) only to be told that wi's do not need trapped, and to just remove it!
I looked around at the other units and to my surprise, not a one was trapped.
To this day I've yet to see another trapped wi, so I took this as a solid! Even prefab polar kings have no trap around here!
Have I been decieved?
sent from my Samsung Galaxy NoteMember of the "Work Exchange Program"
"Will work for knowledge"
"Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
A Einstein
-
03-05-2013, 11:03 AM #33
From your description of the trap you removed, it was located inside the freezer, which is a no-no...however all walk-in evaps require drain traps.
If the trap is located in an ambient which can see below freezing temperature...such as with an outdoor walk-in...the trap must be heated to prevent freezing.
Here's a link to Heatcraft's I&O Manual. (See p.9):
http://www.heatcraftrpd.com/products...5CH-IM-64L.pdf
-
03-05-2013, 01:15 PM #34Member of the "Work Exchange Program"
"Will work for knowledge"
"Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
A Einstein
-
03-25-2013, 04:40 PM #35
Professional Member
- Join Date
- May 2010
- Location
- Brooklyn, NY
- Posts
- 87
i would do the following steps in order:
1) check proper refrigerant charge, if correct go to next
2) check defrost heating element, if good, next
3) check timer, see if it's stuck on refrigeration cycle, see if it goes into defrost cycle, make sure you set enough time for it to defrost
4) check defrost termination relay, if it shows continuity regardless of the temperature, that means it will cause the timer to get back to the refrigeration cycle as soon as the defrost cycle starts, which means u wont get defrost. if it shows no continuity regardless of temperature (although this case is less important, but it will be bad for the compressor overtime), it means IF the evaporator gets too hot on defrost cycle, it won't trip and go back to the refrigeration cycle, which means the compressor will work harder in the start to get it down to the temperature
-