Results 14 to 16 of 16
    Jan 2013
    Henry county,ky
    I ran a gas line last year and caught a whiff when I was done. I had struggled slightly when lining up the union and thought I would check there first. But I said this out loud and before I could move the senior tech had his lighter out and lit the small leak at the union. Nice little blue flame.
    The senior tech I was under years ago did that in a church attic. Wasn't a lot of room to move, needless to say I almost made a new access hole when he pulled out his lighter. First time I had ever seen that, didnt know what to expect.
    " dirty filter??!!! Buts its only 2 years old" You never learn everything you need to know is this industry
    maple ridge, bc
    I did that once, didn't have any elbows left. It looked tacky but was completely legal and safe.
    S.E. Pa
    2009 IRC G2419.4 Sediment trap. Where a sediment trap is not incorporated as part of the appliance, a sediment trap shall be installed downstream of the appliance shutoff valve as close to the inlet of the appliance as practical. The sediment trap shall be either a tee fitting having a capped nipple of any length installed vertically in the bottom-most opening of the tee or other device approved as an effective sediment trap. Illuminating appliances, ranges, clothes dryers and outdoor grilles need not be so equipped.
    Aside from testing for gas leaks with an open flame being illegal per the code and the obvious insanity, it is worthless for leaks under 44,000 ppm NG or 21,500ppm LPG since those are the lower flammability limits. Leaks under these levels can NOT be detected by an open flame.