    documentation on flakers

    Yesterday i got called out to a warrenty call on a scotsman unit. Ive never touched a flaker machine before.

    It was giving me a error code 3 for a empty water resivour and was running water through and down the drain. With help of tech support decided to replaced the lower water seal. He said i can get instructions off scotsman website.

    Why on this unit does it not have a water solenoid?

    I dont have a model number with me but it was the newer prodigy series
    You can't kiss death without it kissing you back. Death is a passionate kisser.


  2. #2
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,719
    Post Likes
    Obviously there is a float valve if not a water inlet valve? I prefer a mechanical float valve over a water inlet valve anyways. Much simpler and doesn't require any water probe sensors to regulate water level. Usually just has a safety probe to shut machine down in case of loss of water.

  3. #3
    Join Date
    Jun 2012
    Location
    Tenn
    Posts
    167
    Post Likes
    Scotsman with CM3 use an electronic water level sensor.

  4. #4
    Join Date
    Feb 2009
    Posts
    209
    Post Likes
    Flakers require a gonstant water level. They make ice continuously therefore using water continuously. A solenoid valve would cause problems not a solution.

  5. #5
    Join Date
    Mar 2006
    Posts
    1,135
    Post Likes
    Thread Starter
    What about when it has a full bin.

  6. #6
    Join Date
    Feb 2009
    Posts
    209
    Post Likes
    The float valve shut stopping the water flow. If it doesn't replace the valve

  7. #7
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    1,022
    Post Likes
    Hoshi flakers have water inlet solenoid valves as their primary water control. Some other machines have a solenoid, and some have a solenoid AND a float.

  8. #8
    Join Date
    Feb 2009
    Posts
    209
    Post Likes
    A solenoid on a scotsman flaker would be an added cost that would add extra service and unnecesary electrical consumption. Float valves are a proven system. They are used in toilets, cooling towers Cattle waterers,etc. Keep it simple stupid is sound engineering

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •