    Carrier secondary

    I was on a call a month ago and had a 12 yo weather maker leaking water. There was no water leaking out of any drain lines, hoses or anything. Only water coming from the blower motor opening. Inducer was mounted one 90 degree turn to the right from up venting out the side. A wall was built 8" in front of the furnace so no pulling the blower. Can anyone shed light on where the water was leaking from? I called rotten secondary but the homeowner dismissed me.







    Only perfect practice makes perfect.

  2. #2
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,589
    If that's the gray box they have bad secondary's all the time, junk

  3. #3
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,135
    HX is done. Pull the blower next time!

  4. #4
    Join Date
    Jan 2011
    Location
    Ottawa, Canada
    Posts
    398
    Quote Originally Posted by syndicated View Post
    HX is done. Pull the blower next time!
    +1

    Sent from my GSIII on Tapatalk

  5. #5
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    3,579
    Quote Originally Posted by syndicated View Post
    HX is done. Pull the blower next time!
    Right after they take out the wall, maybe.

    Itstartedasacc = it started as a clean and check? Clever...and unfortunately an appropriate phrase at times.

  6. #6
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    4,408
    failed h/x is your answer. lots of them rotted away at the front portion.

  7. #7
    Join Date
    Jan 2011
    Location
    Ottawa, Canada
    Posts
    398
    Quote Originally Posted by gravity View Post
    failed h/x is your answer. lots of them rotted away at the front portion.
    I have found some by pulling the limit and using my camera to look straight down at the front and back of the secondary. Look for white deposits on the fins and at the ports.
    May save pulling the blower.

    Or if you have room. You can pull thhe ventor and collector box and look at the ports of the secondary.

    Sent from my GSIII on Tapatalk

  8. #8
    Join Date
    Dec 2005
    Posts
    94
    Another indirect check is CO in the exhaust. Bad secondary will result in 200ppm or much more. Normally under 50ppm. May also be some in the house, but not necessarily.

  9. #9
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,813
    probably a bad secondary and they suck to replace ,if you do repair the unit make sure you get all the parts because none of the parts can be reused , replace furnace if possible
    We really need change now

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event