    Carrier secondary
    I was on a call a month ago and had a 12 yo weather maker leaking water. There was no water leaking out of any drain lines, hoses or anything. Only water coming from the blower motor opening. Inducer was mounted one 90 degree turn to the right from up venting out the side. A wall was built 8" in front of the furnace so no pulling the blower. Can anyone shed light on where the water was leaking from? I called rotten secondary but the homeowner dismissed me.
    Only perfect practice makes perfect.
    May 2012
    Upper Michigan
    If that's the gray box they have bad secondary's all the time, junk
    Calgary, Alberta
    HX is done. Pull the blower next time!
    Jan 2011
    Ottawa, Canada
    Quote Originally Posted by syndicated View Post
    +1
    Sent from my GSIII on Tapatalk
    Nov 2011
    St. Louis
    Right after they take out the wall, maybe.
    Itstartedasacc = it started as a clean and check? Clever...and unfortunately an appropriate phrase at times.
    Jul 2009
    Columbia, MD
    failed h/x is your answer. lots of them rotted away at the front portion.
    Jan 2011
    Ottawa, Canada
    Quote Originally Posted by gravity View Post
    I have found some by pulling the limit and using my camera to look straight down at the front and back of the secondary. Look for white deposits on the fins and at the ports.
    May save pulling the blower.
    Or if you have room. You can pull thhe ventor and collector box and look at the ports of the secondary.
    Another indirect check is CO in the exhaust. Bad secondary will result in 200ppm or much more. Normally under 50ppm. May also be some in the house, but not necessarily.
    Virginia
    probably a bad secondary and they suck to replace ,if you do repair the unit make sure you get all the parts because none of the parts can be reused , replace furnace if possible
    Go Trump