    need a condensing unit for a weber coffin type freezer.(weber)

    weber is out of business and the condensing unit is wrong and really old heres some numbers:

    unit: weber coffin type freezer # C-TV-12IC/ Ser#1R102816
    compressor is a 90-1.50 a medium temp compressor

    the condensing unit really needs to be trashed..freezer is 60' away from condenser and line sets are under ground.

    like all my customers this guys broke.

  2. #2
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    12,719
    Post Likes
    I couldn't even find a mention of Weber, so no info seems likely.

    Based on single deck frozen food or ice cream case from 30 years ago, they generally required 450-500 Btuh/ft so between 5400-6000 Btuh at -25ºF SST for frozen foods (or -35ºF SST for ice cream) should work OK for a 12 footer.

  3. #3
    Join Date
    Jun 2005
    Location
    Las Vegas NV
    Posts
    1,199
    Post Likes
    Quote Originally Posted by primmers View Post
    unit: weber coffin type freezer # C-TV-12IC/ Ser#1R102816
    compressor is a 90-1.50 a medium temp compressor
    Is this a Copeland semi-hermetic compressor? If so it is from the 60's with that part number 90-150. The current compressor number is an EAB?-015A-??? which is a MT12 or LT502 compressor.

  4. #4
    Join Date
    May 2005
    Posts
    1,581
    Post Likes
    Thread Starter
    this icemeister ill look for one..

  5. #5
    Join Date
    May 2005
    Posts
    1,581
    Post Likes
    Thread Starter
    yes powell it is a semi compressor, this place is a mess, and was put together with junk
    he knows i won't continue the practice..and will replace the condensing unit with what is correct..

  6. #6
    Join Date
    Jun 2005
    Location
    Las Vegas NV
    Posts
    1,199
    Post Likes
    The 90-150 (EAB-0150) is a MT12/LT502 compressor as I stated but the LT502 use is an alternative application for which I cannot find any btuh specs.

    Based on it's CFH and the S.W.A.G theory I would guess it's LT502 btuh's are very close to what Icemeister listed.

  7. #7
    Join Date
    May 2005
    Posts
    1,581
    Post Likes
    Thread Starter
    got a quote today for $2755,,,,MY CUSTOMER IS GOING TO COUGH UP HIS LIVER..

  8. #8
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    12,719
    Post Likes
    I've had very good experience with the newer hermetic low temp units...and they save a boatload of money.

    Look at a Copeland FJAL-B301-TFC.

  9. #9
    Join Date
    May 2005
    Posts
    1,581
    Post Likes
    Thread Starter
    wii do, thanks.

  10. #10
    Join Date
    May 2005
    Posts
    1,581
    Post Likes
    Thread Starter
    Quote Originally Posted by icemeister View Post
    I've had very good experience with the newer hermetic low temp units...and they save a boatload of money.

    Look at a Copeland FJAL-B301-TFC.
    ice, i cut find any info on this model number..

  11. #11
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    12,719
    Post Likes
    Quote Originally Posted by primmers View Post
    ice, i cut find any info on this model number..
    Here's a link to the Copeland info (See p.9): http://www.hvacrinfo.com/CopelandUni...DS-4_MandF.pdf

  12. #12
    Join Date
    May 2005
    Posts
    1,581
    Post Likes
    Thread Starter
    wow a 3 hp system.....Ok, thanks..

  13. #13
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    12,719
    Post Likes
    Quote Originally Posted by primmers View Post
    wow a 3 hp system.....Ok, thanks..
    A 3 HP unit does appear to be big for this application...if you're comparing it to what the semihermetics will do...but going by the estimated loads I stated of 5400-6000 Btuh at -25ºF SST for frozen food (or -35ºF for ice cream) the FJAL-B301 would be the one to go with.

    While the FJAL-A225, at a rated 5380 Btuh at -25ºF SST is a tad shy of what we need for FF, it's close enough that it might work OK...but I'd feel a lot better with a little extra, especially when you consider that we're taking a wild guess at what the load really is for that old case.