    R410A Burnouts

    Has anyone run across many 410a burnouts? I am just wondering if the old smell the freon to check burnouts still applies, or if there is a better way to do it in hte field? Also with a 410 burnout does the lineset need changed regardless of severity?

  2. #2
    Join Date
    Aug 2012
    Posts
    2,663
    You don't need to change the lineset just apply normal cleanout functions like purging with nitrogen and a suction liquid line FD, they even have a solvent you can flush it with. You can get an acid check kit too.
    My name is TooCoolforschool and I am a chronic over charger.

  3. #3
    Join Date
    Jan 2013
    Location
    Texas
    Posts
    33
    Ok Thanks. I had someone trying to tell me with 410a that the lineset had to be changed no matter how bad a burnout, and wasnt looking forward to breaking that to the customer.

  4. #4
    Join Date
    Aug 2012
    Posts
    2,663
    Just flush it out.
    My name is TooCoolforschool and I am a chronic over charger.

  5. #5
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,595
    Quote Originally Posted by TXTech1 View Post
    Ok Thanks. I had someone trying to tell me with 410a that the lineset had to be changed no matter how bad a burnout, and wasnt looking forward to breaking that to the customer.
    Did they explain their reasoning for that??

  6. #6
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,179
    Yea I'd also like to hear the reasoning .... ask the guy further info because im sure we'd all love to hear what he said !

  7. #7
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    3,980
    flush it out real good with a bottle or 2 of nitrogen. put oversized hh driers on them. add some acidaway if you want. and make sure there is a pressure tap on both sides of the suction and liquid drier so you can check PD

  8. #8
    Join Date
    Feb 2013
    Location
    New Jersey before and after Texas
    Posts
    65
    Quote Originally Posted by toocoolforschool View Post
    You don't need to change the lineset just apply normal cleanout functions like purging with nitrogen and a suction liquid line FD, they even have a solvent you can flush it with. You can get an acid check kit too.
    Carrier suggested through a memo last summer not to use the flush on their units upon changing over to 410a or cleaning lines due to the residue that coats seals and keeps them from being oiled during operation.

  9. #9
    Join Date
    Feb 2013
    Location
    New Jersey before and after Texas
    Posts
    65
    Quote Originally Posted by gravity View Post
    flush it out real good with a bottle or 2 of nitrogen. put oversized hh driers on them. add some acidaway if you want. and make sure there is a pressure tap on both sides of the suction and liquid drier so you can check PD

    Flushing with nitrogen is recommended and injecting hemoglobin is my brainstorm idea.. I guess they need to watch the money because of those beautiful Bristols..

  10. #10
    Quote Originally Posted by Joseph'bidness View Post
    Flushing with nitrogen is recommended and injecting hemoglobin is my brainstorm idea.. I guess they need to watch the money because of those beautiful Bristols..
    Hemoglobin injection?

    This is a condenser line set, not a vampire-bat.

  11. #11
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,179
    Maybe he meant Hemotobin

  12. #12
    Join Date
    Oct 2010
    Location
    AZ
    Posts
    646
    Isn't injecting hemoglobin one of the things that Lance Armstrong did? I never heard of blood doping an ac unit.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event