  1. #53
    Join Date
    Dec 2011
    Location
    Rio de Janeiro, Brazil
    Posts
    23
    Quote Originally Posted by johnnymick View Post
    Midwest or GA,

    I can't find the thread with the video you mentioned... can you post a link?

    Thanks.
    http://hvac-talk.com/vbb/showthread....1#post15346851

  2. #54
    Join Date
    Dec 2011
    Location
    Rio de Janeiro, Brazil
    Posts
    23
    Quote Originally Posted by midwesthvactech View Post
    Not busting your balls ga-tech but do you recall where you saw that article. I would love to have it for our next service meeting. We have guys who pull 100 micron and lower vacuums.

    I personally do 1000 break with nitro and down to 450 - 400.

    http://www.jbind.com/pdf/Deep_Vacuum.pdf

    "There are many recommendations regarding evacuation levels, some of which state: “Evacuate the system to below 200 microns.” This should not be considered. Note that the word “system” is used here, because it is possible to evacuate piping or some component other than the compressor to below
    this level. Refrigeration oil has a vapor pressure and, by going below 200 microns, you will degas particles of the refrigeration oil. Be aware that if you change the makeup of the oil, it will no longer be a true lubricating oil."

  3. #55
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,957
    Refrigeration oil has a vapor pressure and, by going below 200 microns, you will degas particles of the refrigeration oil. Be aware that if you change the makeup of the oil, it will no longer be a true lubricating oil.
    While technically true, I don't think that the average tech should worry themselves over-much about this.

    Just like dehydrating a system with a vacuum pump, it's about micron level and TIME.

    The TIME factor is often ignored.

    If you left your pump on it, running, at a vacuum level of 100 microns for 10 minutes, 15 minutes, 30 minutes; I don't see you removing enough of these additives to create a problem.

    If you left that pump running for days on end at the same vacuum level...

  4. #56
    Join Date
    Nov 2008
    Location
    DFW,TX
    Posts
    2,211
    im not sure brand unless i go look but i think YJ 2 stage 6cfm and i have two ones 15 yrs old and my backup but still works great and this one is like 5 yrs old and again works great..

  5. #57
    Join Date
    Feb 2013
    Location
    Summerville SC
    Posts
    117
    update for those who were enlightened me to read up on properly evacuating a system. My 2 appion megaflow basic kits came in Friday. I also got my new yj superevac 6 cfm. I also picked up a vacuum tree until I can get a chance to find or make a tee fitting to just fit to my pump...mainly because the tree has multiple places it could leak and is so daggum bulky and awkward. I have 2 indoor coil changeouts to do Wednesday so I will add another reply with the results of the new setup. on average with a fair length lineset it would take me around a hour to a hour and a half to pull into 300-400 range with valve cores removed through 1/4 hoses. Im really hoping to see a very great decrease in time to pull a good vacuum. thanks again for all the recommendations and advice.

  6. #58
    Join Date
    Mar 2006
    Location
    Denver/Boulder
    Posts
    2,420
    Don't forget to apply for pro staus now that you hit 15 posts. Just be prepared to wait. It takes a LONG while for most.
    What lies behind us and what lies before us are small matters compared to what lies within us.


    Two pressures, four temperatures = SUCCESS!


    Boulder Heating Contractor


    For Consumers:

    For HVACR Professionals:


  7. #59
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    21,766
    Quote Originally Posted by SCtech33 View Post
    update for those who were enlightened me to read up on properly evacuating a system. My 2 appion megaflow basic kits came in Friday. I also got my new yj superevac 6 cfm. I also picked up a vacuum tree until I can get a chance to find or make a tee fitting to just fit to my pump...mainly because the tree has multiple places it could leak and is so daggum bulky and awkward. I have 2 indoor coil changeouts to do Wednesday so I will add another reply with the results of the new setup. on average with a fair length lineset it would take me around a hour to a hour and a half to pull into 300-400 range with valve cores removed through 1/4 hoses. Im really hoping to see a very great decrease in time to pull a good vacuum. thanks again for all the recommendations and advice.
    My Appion TEZ8 could pull that vacuum through a Titan 2 manifold in less than 30 min... maybe 20 min if the lineset was relatively clean inside... might even make 250 microns. I left it on a 50'~ lineset and 4 ton AH for an hour... had something like 150 microns... through a manifold. (Note the manifold does have a 3/8 vacuum hose).
    GA-HVAC-Tech

    Quality work at a fair price with excellent customer service!

    Romans Ch's 5-6-7-8

    2 Chronicles 7:14

  8. #60
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,957
    Quote Originally Posted by SCtech33 View Post
    update for those who were enlightened me to read up on properly evacuating a system. My 2 appion megaflow basic kits came in Friday. I also got my new yj superevac 6 cfm. I also picked up a vacuum tree until I can get a chance to find or make a tee fitting to just fit to my pump...mainly because the tree has multiple places it could leak and is so daggum bulky and awkward. I have 2 indoor coil changeouts to do Wednesday so I will add another reply with the results of the new setup. on average with a fair length lineset it would take me around a hour to a hour and a half to pull into 300-400 range with valve cores removed through 1/4 hoses. Im really hoping to see a very great decrease in time to pull a good vacuum. thanks again for all the recommendations and advice.

    http://youtu.be/eGLYAmjWkvA

    Just showing what a good setup can do for your evacuation time.

  9. #61
    Join Date
    Feb 2013
    Location
    Summerville SC
    Posts
    117
    Quote Originally Posted by jpsmith1cm View Post
    http://youtu.be/eGLYAmjWkvA

    Just showing what a good setup can do for your evacuation time.
    this is the video that opened my eyes and what convinced me to purchase the megaflow basic kits.the full kits are out of my price range after the vacuum pump but next money to come in ill be ordering the bluvac gauge. Thanks for the info to!

  10. #62
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,957
    Quote Originally Posted by SCtech33 View Post
    this is the video that opened my eyes and what convinced me to purchase the megaflow basic kits.the full kits are out of my price range after the vacuum pump but next money to come in ill be ordering the bluvac gauge. Thanks for the info to!
    Build your own kit, piece by piece as you can afford it.

    I don't have a full mega-flow kit, either.

  11. #63
    Join Date
    Feb 2008
    Location
    Waffleville
    Posts
    10,339
    Quote Originally Posted by ga-hvac-tech View Post
    My Appion TEZ8 could pull that vacuum through a Titan 2 manifold in less than 30 min... maybe 20 min if the lineset was relatively clean inside... might even make 250 microns. I left it on a 50'~ lineset and 4 ton AH for an hour... had something like 150 microns... through a manifold. (Note the manifold does have a 3/8 vacuum hose).
    yeah, because 8cfm isn't overkill <G>
    If Guns Kill People, Do Pencils Misspell Words?

    http://www.youtube.com/watch?v=An2a1...eature=related

    Before we work on artificial intelligence why don't we do something about natural stupidity?

  12. #64
    Join Date
    Feb 2008
    Location
    Waffleville
    Posts
    10,339
    Quote Originally Posted by jpsmith1cm View Post
    Build your own kit, piece by piece as you can afford it.

    I don't have a full mega-flow kit, either.
    don't need to buy a full magnaflow kit... if you know which parts and pieces to buy
    If Guns Kill People, Do Pencils Misspell Words?

    http://www.youtube.com/watch?v=An2a1...eature=related

    Before we work on artificial intelligence why don't we do something about natural stupidity?

  13. #65
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,957
    Quote Originally Posted by beachtech View Post
    don't need to buy a full magnaflow kit... if you know which parts and pieces to buy
    This is true.

    It also depends on what pump you use and what equipment you're working on.

    I'm good to go with 3 x 3/8" hoses off of a 7CFM pump. I've also got 2 VCRTs that I don't typically use both of because I've got service valves to use.

Page 5 of 6 FirstFirst 123456 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event