02-24-2013, 04:05 PM #1
craft 2 ton heating mode problem
hi
i have 2 ton craft split unit
it had leak so i repair it
when i charged the system
it work peftectly in cooling mode
11 a current
40 psi suction line pressure
but when i change it to heating mode
the discharge pressure increases gradually
starting from
8 ampere
100 psi
reaching 475 psi
and current reach 25 a
so compressor start opening relief valve
so pressure decrease to 350 psi then increase to 475 psi
so what is the problem
i checked both capillary tube and filter in outdoor unit they are working very good
voltage is 220 v
can it be blockage in the indoor unit
-
03-04-2013, 02:38 PM #2
up
-
03-04-2013, 06:47 PM #3
40 psi seems a little low! Maybe your indoor coil is packed with dirt!!!!
-
03-04-2013, 06:51 PM #4
What refrigerant are you using.
-
03-05-2013, 07:00 AM #5
maybe insulation came off indoor unit and blocking coil
-
03-05-2013, 10:29 AM #6
-
03-05-2013, 10:33 AM #7
-
03-05-2013, 10:35 AM #8
-
03-05-2013, 03:47 PM #9
-
03-05-2013, 04:46 PM #10
Does the indoor unit have options for fan speeds ?
When you turn on heat , make sure the fan is blowing on high
Never heard of a Craft .... but on older units , the insulation inside the air handler itself will begin to fall apart after years of operation.
-
03-06-2013, 02:08 PM #11
-
03-06-2013, 02:11 PM #12
-
04-30-2013, 10:06 AM #13
the cause was reversing valve
i changed it