Results 1 to 13 of 13
    Aug 2012
    Iraq
    craft 2 ton heating mode problem
    hi
    i have 2 ton craft split unit
    it had leak so i repair it
    when i charged the system
    it work peftectly in cooling mode
    11 a current
    40 psi suction line pressure
    but when i change it to heating mode
    the discharge pressure increases gradually
    starting from
    8 ampere
    100 psi
    reaching 475 psi
    and current reach 25 a
    so compressor start opening relief valve
    so pressure decrease to 350 psi then increase to 475 psi
    so what is the problem
    i checked both capillary tube and filter in outdoor unit they are working very good
    voltage is 220 v
    can it be blockage in the indoor unit
    Aug 2012
    Iraq
    up
    Phoenix,AZ
    40 psi seems a little low! Maybe your indoor coil is packed with dirt!!!!
    What refrigerant are you using.
    Virginia
    maybe insulation came off indoor unit and blocking coil
    Aug 2012
    Iraq
    Quote Originally Posted by KB Cool View Post
    i cleaned it
    and i charged it to 50 psi
    Aug 2012
    Iraq
    arkime freon 22
    Aug 2012
    Iraq
    Quote Originally Posted by Snapperhead View Post
    can you explain more
    May 2011
    Western, KY
    Quote Originally Posted by kefah View Post
    hi
    11 a current
    starting from
    8 ampere
    100 psi
    reaching 475 psi
    voltage is 220 v
    Kefah you have enough posts to apply for pro membership, in the locked pro forum you can get detailed technical info for anything you ask.
    Virginia
    Does the indoor unit have options for fan speeds ?
    When you turn on heat , make sure the fan is blowing on high
    Never heard of a Craft .... but on older units , the insulation inside the air handler itself will begin to fall apart after years of operation.
    Aug 2012
    Iraq
    Quote Originally Posted by mason View Post
    thanx
    i will try it
    Aug 2012
    Iraq
    yes i choose high speed
    but it automatically
    start with low speed then full speed
    Aug 2012
    Iraq
    the cause was reversing valve
    i changed it