Building a new home..2 units OR 1 unit with zoning? Newbie needs help..
First off, I am an HVAC newbie so forgive me if I don't use the correct terminology below. Here we go..
I am having a home built this spring. The home is about 3200 sq ft. 1600 on each floor. Attached floorplans. It will have an electric heat pump with propane backup. I am in southeast PA. I also plan to run a wood burning stove to supplement heat in the winter, although I know this shouldn't affect the HVAC design.
I'm wondering if such a house needs 2 different heating/cooling units (I assume one in basement and one in attic) or does it just need one bigger unit, but with some kind of zone setup where dampers open and close the ductworks based on different thermostats?
My understanding is that the builder will send the houseplans to the HVAC folks (he says he sends them to York) and they will come up with the best HVAC plan. I know they should use a manual J to figure things out, but how do I know that their decision is the right one? i.e. how do I know the builder doesn't say to use just one unit b/c he wants to save money?
So my questions are:
1. For such a home, just looking at the floorplans, does it appear I would need 2 units or just 1 unit with zoning?
2. How does one make sure the builder's decision is the right one? I plan to be in the home for the long haul, and I've heard over and over to make sure they get the HVAC and ducting done right.
Thanks in advance!
-
02-22-2013, 11:34 PM #2
A1: I would venture to say that you would get two systems, and two would be the better design than one system for a few reasons.
A2: NOT ONLY YES, BUT HELL YES!
Just like anything else, get a second opinion (and maybe a third), and see if you can get two (or may three) matching designs.
There is a lot that goes in to a system to make sure you achieve optimum comfort control.
When building, the biggest thing you can do to ensure you achieve optimum comfort control is: don't skimp on the insulation, and windows and doors.
I don't care how great your system is, with out proper insulation, and good window and doors you are pissing in the wind.
Please watch this video, one of the best ones out there imo.The opinions expressed by me are not that of my employer.

-
02-23-2013, 07:20 AM #3
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,762
I would probably opt for 2 separate systems to keep the air noise down (two 3 ton vs one 5 ton blower). I like geothermal system(s) but I also like the foam insulation. I would do some load calculations (to find the payback) as to the best bang for the buck.
Remember, the better insulated home requires smaller HVAC. So the extra money spent on insulation saves on the cost of the HVAC equipment.
-
02-23-2013, 07:32 AM #4
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,762
One other thought........I would keep all a the HVAC out of the attic. Equipment and ductwork.
-
02-23-2013, 07:35 AM #5
If you put a system in the attic, the attic roof must be insulated to avoid condensation problems with ducts winter and summer.
Also fresh air ventilation is a must. YOu need a fresh air change in 4-5 hours when occupied to purge indoor pollutants and renew oxygen. A simple reliable device for thiw is a whole house ventilating dehumidifier like the ULtra-Aire. This will provide filtered fresh air to the whole house and maintain <50%RH during wet times of the year.
Regards TBBear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
02-23-2013, 07:53 AM #6
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,275
FIRST
Thermal Envelop Spec
Ceiling R-45 ... spray foam on underside of roof ... ALL ducts in conditioned space
Walls R-16
Windows U < 0.3
Air Change per Hour (A.C.H.) < 0.25
MAX flex duct length 9 feet
ACCA Manuals J & D -
-- approved by PA Professional Mechanical Engineer (ME)
-- thermal envelop, HVAC equipment and duct work inspected and accepted by PA ME
HRV at ~ 60 CFM per floor
http://www.broan.com/products/lifest...f-d721c95ad1a0
Builder needs to Guarantee performance < 16,000 BTU/Hr @ 10'F per floor.
Strip emergency heat - 2 kW [2]/ Floor
Operating cost of strips to be paid by builder - part of the performance Guarantee
SECOND
2 Units
Page 42
http://www.upgnet.com/PdfFileRedirec...ytg-a-0410.pdf
http://www.paelectricrates.com/cityp...ntown&state=PA
http://www.climate-zone.com/climate/...nia/allentown/Last edited by dan sw fl; 02-23-2013 at 08:14 AM. Reason: + PA rates
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
02-23-2013, 08:19 AM #7
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,275
i.e. PECO $0.096 / kW-Hr after 1Apr13
http://www.papowerswitch.com/shop-fo...eco-energy/rh/
Builder and mechanical contractor/HVAC should pay any electric cost for heating > $600 / year for 10 years
( pro-rated to $0.096 / kW and 5,000 Heating Degree Days [ HDD])
If there are only 4,000 HDD in a Winter season, any annual electric heat cost > $480 to be paid by builder/ HVAC installer.
........................6,000 HDD .................................................. ..................> $720 ........."....... " .......... "...............Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
02-23-2013, 08:43 AM #8
If it were my house I would not even consider having one system zoned. Two systems is the way to go. The only reason to put in one system would be to save on the initial cost of installation. Compared to the cost of building the whole house it is a minimal savings with much more possible negative consequences than positive.
Gary
-----------
http://www.oceanhvac.com
An engineer designs what he would never work on.
A technician works on what he would never design.
-
02-23-2013, 10:18 AM #9
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,275
Fan Installation
For any additional ventilation needs, make Sure your installer is Fully qualified.
http://blip.tv/eyehandy/how-to-insta...vannah-5471801
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
02-23-2013, 11:40 AM #10
Professional Member
- Join Date
- Feb 2013
- Location
- Sonora, CA
- Posts
- 147
This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.
You can find the rules for posting and qualifications here.
Additional infractions may result in loss of posting privileges.
Last edited by jpsmith1cm; 02-23-2013 at 12:38 PM. Reason: non AOP Member
-
02-23-2013, 11:53 AM #11
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,275
Zoning co$t is NOT Negligible. I am not a contractor, but - one might guess that zoning $$$ might be 'in the range
of half' of a second system. So, ... where's the Real savings __ only 'A FEW $$$'s' in the builder's pocket.?!
How many actually know how to install & set-up properly.
How much tweaking is generally done ( + paid by HomeOwner $$$) to satisfy the customer's comfort level over the first few years of operation?!Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
02-23-2013, 12:38 PM #12
jacob-k
This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.
You can find the rules for posting and qualifications here.
Additional infractions may result in loss of posting privileges.
-
02-23-2013, 02:16 PM #13
Professional Member*
- Join Date
- Jan 2002
- Location
- East Grand Forks, MN
- Posts
- 1,361
I vote for one system.
If you know how to design, then it should not be a problem with only one system, especially when you mentioned a dual-fuel set up... you have your backup already built-in!
Why two, it's not very green or cost effective? More energy is used up and each system will probably be oversized a bit due to the equipment limited small sizes manufactured.
If your serious, then forget the equipment in the attic idea. Sized the duct/s correctly, never ovesize, and seal everything: ducts, house etc...
and don't forget a good fresh-air system....
Note: the only time I would install two systems is when they need more than 5 tons of cooling.


Reply With Quote