    Talking Trusteam!!!

    Guys,

    Another one. I recently went to a house where someone installed 3 trusteams. The house is roughly 4500 square feet. There is 3 HM506 6 gallon trusteams in there. It could not keep up with the 40% humidity this customer wanted in there. After talking to Honeywell, the guy told me to basically throw their chart out the window and go by feel. He suggested just adding another trusteam to raise humidity more. He also explained to me that the more wood and sheetrock, anything but metal and glass, that was in the house, the more humidity you will need. The house has a a ton of 4' poplar trim along all the walls on the first floor, and a mahogany trey ceiling on the second floor. Hardwood floor throughout as well, except for bathrooms. The heating system is all radiant in floor heat. I control the air handlers and trusteams with prestige t-stats. The house is fairly tight as well, 2x6 walls, but not foamed. I am not looking for an exact answer, I know that is impossible without al the info, but again, your thoughts, thanks. Hoping to see the tedbear gut on this

  2. #2
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    536
    Post Likes
    Why not 12 gallon units?

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by dunkman View Post
    Why not 12 gallon units?
    Get rid of those toy 6 GPD humidifiers, and put in 3 12 GPD. Plus, recheck your air handlers and duct work for leakage to/from unconditioned space.

    What ID humidity are they holding at what IN temp, and what are the OD temp and RH.

    Basically on a 4500 sq ft house with 8 foot ceilings through out at a .3 ACH with outdoor conditions of 0°F and 40% RH. 3-6 GPD humidifiers would have to run all day, and no one could leave or enter the house or the humidifiers would lose ground as soon as any door was opened. Now throw in their flush/self cleaning time, and your not gonna reach or maintain 40%, which is a fairly high RH to begin with.

  4. #4
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    If 3 6 gallon trusteams can't keep up in that house, then it is not a tight house.

    They should fix the house rather than keep throwing humidity at it. I have 2800 sq ft conditioned space and went from a AA fan powered humidifier running almost steady, to leaving it shut off and still maintain 30-40% RH. All I did was seal air leaks on the attic and rim joists.

  5. #5
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    I agree. Fix the leaking house. I have 3200 SF and a 9 GPD. RH is hanging at 37% with very little humidifier run time.

    Quote Originally Posted by chuckcrj View Post
    If 3 6 gallon trusteams can't keep up in that house, then it is not a tight house.

    They should fix the house rather than keep throwing humidity at it. I have 2800 sq ft conditioned space and went from a AA fan powered humidifier running almost steady, to leaving it shut off and still maintain 30-40% RH. All I did was seal air leaks on the attic and rim joists.
    Perhaps you should have read the instructions before calling.

  6. #6
    Join Date
    Jul 2010
    Location
    NJ
    Posts
    139
    Post Likes
    Thread Starter
    that's what we are going to do tomorrow, put a 12 on first floor and take it from there.

  7. #7
    Join Date
    Jul 2010
    Location
    NJ
    Posts
    139
    Post Likes
    Thread Starter
    Orignal installer told the guy he put in 3 9 gallon. Did not want to tell the guy to just throw in 12 gallon humidifiers and spend more money. Also was under the impression from a honeywell class I went to, promoting the trusteam, you do not want to go overboard with sizing them. I suppose the house is not as tight as I think, owner assures me everything was insulated well and sealed up. He was a commercial roofer, and built the house, so took that info a little more serious then I normally would. As far as indoor temp, it stays at 68, indoor humidity varied by area. The first floor seems to sat around 27 - 30 % indoor humidity, and outside varies, not really sure. The second floor stays around 35, but there are 2 6 gallon units up there on two different AHU. I am in central/south NJ, so it stays around 20 - 50 in the winter. Ceilings are ten feet. Agree to that the 40% is a little high, but got him down to that from the 45% he wanted. I figure he can set the humidity at what he wants, if that is what is comfort to him and he is not going to far off the map. Thanks for the input guys.

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Does the house have a fresh air intake/HRV/ERV?

    10 foot ceiling. That brings it up to needing almost 5.5 pounds of moisture per hour at 20° OD temp and 20% OD RH. So those 3-6 GPD can only put 6.25 pounds an hour. So again anytime a door is opened, the humidity is gone.

    The 3-6 GPD are too small. Get a 12 put on at least the first floor system.

  9. #9
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    Not being a basher here...but I am sure anyone with experience with the TruSteam will tell you to save yourself the heartache, future warranties, and an upset customer and throw the TruSteam in the garbage. Look into the AprilAire 800 series and have a nice issue free relationship with the equipment and your customer.

  10. #10
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Get rid of the truesteams. They are @&%&#&^@@ JUNK!....Sorry, my tourettes kicked in.

    Go with the aprilaire 800. If wired to 240, they can produce up to 22GPD i believe.

    The trusteams are nothing but trouble. The homeowner will spend a fortune on them before a year of run time and every year after that.

    the aprilaire 800 likes dirty water and maintenance is simple...by replacing a canister or cleaning it out.


    have the homeowner tighten up the house. It leaks too much

  11. #11
    Join Date
    Jul 2010
    Location
    NJ
    Posts
    139
    Post Likes
    Thread Starter
    Gravity,

    Does the Aprilaire 800 allow for remote mounting and if yes what is the distance. I have another client looking for humidifier but can not make it happen with the 20' max allowed by the trusteam, would need aprox. 28 '.

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by Cbssteve View Post
    Gravity,

    Does the Aprilaire 800 allow for remote mounting and if yes what is the distance. I have another client looking for humidifier but can not make it happen with the 20' max allowed by the trusteam, would need aprox. 28 '.
    A Nortec NTHC 20 can have 34 foot of remote hose when installed with an over sized steam pipe.

  13. #13
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    Interesting. I love my TruSteam. Had one client will a failed level sensor on start. No problems beyond that. We sold many.
    Perhaps you should have read the instructions before calling.

  14. #14
    Join Date
    Oct 2004
    Location
    Yakima, WA
    Posts
    1,847
    Post Likes
    Just curious - have you checked the control setup? Is humidification allowed any time, or only when heat is calling? I have run into a couple like this that wouldn't maintain to set point because they would shut down whenever the heat call satisfied.

  15. #15
    Join Date
    Jul 2010
    Location
    NJ
    Posts
    139
    Post Likes
    Thread Starter
    Quote Originally Posted by cjpwalker View Post
    Just curious - have you checked the control setup? Is humidification allowed any time, or only when heat is calling? I have run into a couple like this that wouldn't maintain to set point because they would shut down whenever the heat call satisfied.
    With a call for humidification, the thermostat will put on the fan. Thermostat is a prestige by Honeywell. We made sure it would work and verified by double checking the installer set-up.

  16. #16
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    I found these humidifiers the other day, two of these would work maybe?Name:  ImageUploadedByTapatalk1361741477.316414.jpg
Views: 234
Size:  54.2 KB

  17. #17
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    What beenthere said.

    They are just like an aprilaire

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •