Results 1 to 13 of 20
    Jul 2010
    NJ
    TXV all the time?
    Whenever I put in a 410-a system, I use a TXV. I use 14 seer Goodman equipment as my standard. Every once and a while people ask to shave a couple bucks so I tell them I can drop it to 13 seer. My rep says I can just use the piston, but prefer the TXV for the ease of knowing to do the superheat and sub cooling to what it is. My question is, is this ok and is there any positive/negative to this practice. Any input would be nice, thanks.
    May 2009
    Savannah, Ga/H.H. Island, S.C.
    TXV all the time?
    You can use a fixed orfice (piston) on R410A systems. Perfectly fine. Just make sure to use the correct size.
    Home of the newly wed and the nearly dead
    Quote Originally Posted by Brent Ridley View Post
    But why would you want to? IMO, a TXV is preferable 100% of the time.
    Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
    "It's called the american dream because you have to be asleep to believe it" -George Carlin
    "A nation of sheep begets a government of wolves" -Edward R. Murrow
    "I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
    Buy american made goods & support locally owned businesses!
    Apr 2001
    FL Panhandle
    Get on the goodman website, look up the outdoor unit you are offering, click on the specifications which will bring up the PDF and scroll down to the ahri ratings portion.
    You'll see many 14 SEER matches that use either txv or piston. It's important that your match is the SEER rating you are offering. There will be a different ahri number for similar equipment with differing metering devices.
    I myself prefer a txv, and some utility companies offering rebate $ may require a txv to qualify for their incentive even if the SEER rating is the same with a fixed restrictor.
    May 2009
    TXV all the time?
    Some people are not fans of TXV's. A expansion valve can mechanically fail.
    An orfice can't mechanically fail.
    but it can clog.
    Jun 2009
    Upstate SC
    X2 i did it for several systems because of parker txv issues.
    Sent from my SCH-I510 using Tapatalk 2
    Feb 2013
    I also prefer a TXV, but the piston is ok too. With the piston the correct charge becomes critical.
    Feb 2013
    Florida
    Less things to go wrong with fixed, but as stated above is more charge critical
    I prefer TXVs, very strongly, I just wish they would go back to making them like they did 10 years ago...
    Apr 2001
    FL Panhandle
    I prefer txvs as well... The adjustable kind. The Sporlan kind.
    How many adjustable Sporlans do you see as OEM on resi equipment these days?
    I'm thinking long and hard here on that one.
    Jul 2009
    South Carolina
    I don't think there is any one simple answer to the OP's question. The TXV usually makes a more efficient system but it also has a higher failure rate than a piston. On some Goodman 15 SEER systems the rating is the same with or without a TXV. As for their 13 SEER's, a TXV in place of a piston doesn't seem to change the ratings either. Most Goodman TXV's are adjustable so there is no guarantee the SH is going to be right unless it is tested & fine tuned anyways. I do just the opposite & use a piston instead of a TXV wherever possible on their 15 SEER systems but it really comes down to preference.
    My guess would be that any Goodman factory tech would say that you could always put a TXV on any of their 410A systems.
    Gary
    http://www.oceanhvac.com
    An engineer designs what he would never work on.
    A technician works on what he would never design.
    Tallahassee, FL
    I use a txv when I can also. It is the superior metering device. Not only by controlling constant superheat but providing faster "warmup " time by non bleed txvs.
    Yes they have problems from time to time but I feel like the majority are from external sources
    overheating during brazing
    liquid restriction.
    Jul 2009
    South Carolina
    I've said this before but to reiterate the rhyme:
    "For a more reliable system use a piston, for more efficiency use a TXV"
    Gary