[QUOTE=gravity;15287331]Sounds to be over charged in heating.
You need 450cfm/ton for heating mode.
Where do you get this number? I do heatpumps all the time and have never got them to pull 450cfm/ton and they work great. All specs i have ever seen say 375 -400 a ton is fine. Or am i wrong?
-
02-26-2013, 11:50 AM #16
The SST is warmer than the outdoor air.
The possible causes I can think of are overcharge, metering device over feeding & low indoor airflow.
We can eliminate the outdoor TXV over feeding so there's not much left. I wouldn't be surprised if it had both low airflow & was over charged.Gary
-----------
http://www.oceanhvac.com
An engineer designs what he would never work on.
A technician works on what he would never design.
-
02-26-2013, 06:01 PM #17
-
02-26-2013, 07:46 PM #18
heating needs more airflow because the coil is smaller. look it up
-
02-26-2013, 11:09 PM #19
Professional Member
- Join Date
- Oct 2012
- Location
- Sacramento,ca
- Posts
- 172
I did and in every rheem air handler manual i looked into they show the same cfm for heat or cool mode with a chart that shows cfm compared to static pressure and not one is over 400 cfm/ton and they will even accept as low as 350cfm/ton. Also we are regulated in california by calcerts and they never test for anything over 350cfm/ton period.
Where are you seeing this?