    yeah i thought about the unmatched possibility ill get the m/s numbers but no i got the trurn air with a ductulator duct is sealed and not kinked so i figured it was pretty close thanks for the tip about superheat though. makes sense.
    You figured out return air flow with a duculator?
    Oct 2012
    Sacramento,ca
    [QUOTE=gravity;15287331]Sounds to be over charged in heating.
    You need 450cfm/ton for heating mode.
    Where do you get this number? I do heatpumps all the time and have never got them to pull 450cfm/ton and they work great. All specs i have ever seen say 375 -400 a ton is fine. Or am i wrong?
    Jul 2009
    South Carolina
    The SST is warmer than the outdoor air.
    The possible causes I can think of are overcharge, metering device over feeding & low indoor airflow.
    We can eliminate the outdoor TXV over feeding so there's not much left. I wouldn't be surprised if it had both low airflow & was over charged.
    Gary
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.
    Feb 2013
    Florida
    [QUOTE=Barrettservices;15296451]
    Quote Originally Posted by gravity View Post
    Heat mode calls for the same airflow as cooling. 400 +/- 50 a ton
    Jul 2009
    Columbia, MD
    heating needs more airflow because the coil is smaller. look it up
    Oct 2012
    Sacramento,ca
    I did and in every rheem air handler manual i looked into they show the same cfm for heat or cool mode with a chart that shows cfm compared to static pressure and not one is over 400 cfm/ton and they will even accept as low as 350cfm/ton. Also we are regulated in california by calcerts and they never test for anything over 350cfm/ton period.
    Where are you seeing this?