Results 1 to 13 of 19
    Jul 2011
    high sbcooling in heay low in ac
    hey so i did some maintenance on my parents system and found head pressure at 580 with 34 degrees subcoolingin heat check it at ac on 70 degree day and had 5 degrees in cooling . have correct return air, clean filters clean coils. any ideas txv operational on outdoor unit has me stumped 4 ton unit any input would be appreiated thanks
    Danny
    Jul 2005
    Quote Originally Posted by stemps22 View Post
    Danny
    Looks like an air flow issue despite what you said about air flow. Are you sure the blower was running when you were looking at your gauges? It could be dropping out intermittently.
    Feb 2012
    Ottawa, Ontario Canada
    i would love to help! however your lack of punctuation and lack of information hinders me. Delta T accross both coils, high and low side pressures, superheat and subcoolig are all basic assets when asking for AC help.
    You had a heat pump running in the heat mode on a 70 day?
    What was the indoor temperature?
    Feb 2013
    Florida
    Low indoor airflow, overcharge, possibly both?
    If that heating SC check was done when it was 70 outside, its a wonder it didn't go off on high head.
    Virginia
    if you had a 80 degree return air and 70 degree outdoor temp might be perfect ,also thermostat does not show correct RA temp
    Go Trump
    Jul 2011
    Quote Originally Posted by b-roq View Post
    yeah sorry for lack of punctuataion. like i said i checked the subcooling in ac on a 70 degree day and had low subcooling, however in heat mode on a 40 degree day i had 34 degrees. Since you check heat pumps with txvs rather than pistons in subcooling not superheat i did not include that info. I can get the delta t across coils, however head pressure of 586 on a 40 degree day seemed to me to be problematic one way or another. could be wrong. Fan was running and there is 1670 cfm of return air on a 4 ton unit. and please no comments from people who try to put others down with above quotes to make themselves feel better. No disrespect justr don't have time or patience for it. Thanks
    Danny
    od temp 40
    heat mode
    suction 120
    head 586
    subcooling 34
    410a unit
    4 tons
    Tallahassee, FL
    So you have a outdoor txv ? And a communication variable speed that shows the 1670? Doesn't always mean you are getting it. Not saying that is the problem here though.
    Please provide model and serial of units.
    You should always check the superheat anyway, since it is an indicator of whether the TXV is operating correctly or not.
    Also, what model of indoor and outdoor units?
    The issue could be related to the equipment matchup.
    Jul 2011
    yeah i thought about the unmatched possibility ill get the m/s numbers but no i got the trurn air with a ductulator duct is sealed and not kinked so i figured it was pretty close thanks for the tip about superheat though. makes sense.
    Tallahassee, FL
    This may be a whole nother thread worthy but you how are you using that ductulator?
    Jul 2009
    Columbia, MD
    Sounds to be over charged in heating.
    You need 450cfm/ton for heating mode.
    You will have a higher subcooling in heating mode because the ID coil is smaller then the OD coil.
    You're head pressure is too high in heating.
    What are your pressures when you checked in cooling?
    70* is a little cool. If you had lower head pressures this would be why you have lower SC.
    If airflow checks out and you know charge is good (check in a/c) then i would recommend adding a VPS to the OD fan. Carrier used these back in the day on their 410a h/p. If you turn OD fan off it should lower your head pressure.