When I said the savings is minimal I was comparing it to the cost of buildning a whole house. If it costs 20% less to do a zone sytem & the HVAC costs afre 5% of the cost of building the house then we're only talking about 1% of the total cost & probably even less than that. The only reason builders like to do one zone system is so they can cut costs plain & simple. It has nothing to do with what is best for the house. If the HVAC guy told them it would cost more to do one zone system then the builder would recommend two separate systems.
Gary
-----------
http://www.oceanhvac.com
An engineer designs what he would never work on.
A technician works on what he would never design.
-
02-23-2013, 06:05 PM #16
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,357
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
02-24-2013, 12:10 AM #17
Regular Guest
- Join Date
- Jan 2013
- Posts
- 43
So when you say 2 would be better for a number of reasons, what would they be?
Regarding the 2nd/3rd opinions, how would one do that if the builder is in charge of the HVAC and uses a certain HVAC sub? Does one ask them to go out and get a 2nd opinion, or does the homeowner find that 2nd opinion?
I agree, insulation is key. I am upgrading the Silverline (by Andersen) windows to Andersen 200 series. I am planning on doing 2 inches of spray foam throughout the exterior and attic floor. The house is 2x6 (not 2x4). I am planning on having R50 or so in the attic.
-
02-24-2013, 12:13 AM #18
Regular Guest
- Join Date
- Jan 2013
- Posts
- 43
-
02-24-2013, 12:16 AM #19
Regular Guest
- Join Date
- Jan 2013
- Posts
- 43
-
02-24-2013, 12:32 AM #20
Regular Guest
- Join Date
- Jan 2013
- Posts
- 43
-
02-24-2013, 12:38 AM #21
Regular Guest
- Join Date
- Jan 2013
- Posts
- 43
-
02-24-2013, 12:39 AM #22
all contractors should run a Manual J to properly to identify what system size you should start with. From there I would decide two systems vs. one with zoning. Something else to think about when it comes to a new home is indoor air quality. Start by installing a good 4" filter at the unit. Then way the cost between a base builder grade efficient HVAC system with options for higher efficient ones. I would recommend an indoor unit with a variable speed blower, even the newer non-variable speed ECM blowers are better than a standard blower. When you look at upgrading efficiency and IAQ sometimes the cost to upgrade two vs. one is a factor. A good contractor will help you with your budget, utility consumption and provide comfort and a healthier home.
Get that manual j from your builder from all HVAC contractors and make sure they print out a long form so you can review it and that it follows ACCA standards.
-
02-24-2013, 03:46 AM #23
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,357
3 tons could be TOO Much for proper Thermal Envelope.
You didn't read reply provided in post #6.
Spray foam is recommended for the Underside of the roof.
http://www.buildingscience.com/docum...r-all-climates
ALL DUCTS IN CONDITIONED SPACE.
I guess if you don't control the design and installation,
You Get what You Get
and DON.T Have a Fit.Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
02-24-2013, 07:48 AM #24
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,819
-
02-24-2013, 08:24 AM #25
Regular Guest
- Join Date
- Jan 2013
- Posts
- 43
I have read some about variable speed, in fact was at one point looking at the Greenspeed unit. Even if I don't do that specific unit, I do want to get a more efficient, and overall better, unit even if it does cost a bit more. I will be sure to ask for the manual J printout.
-