  1. #1

    Not making Ice

    Have decent experience in field but still need help at times , sometimes overlook obvious , I have a undercounter Mantitowoc ice machine QY0214A diag bad compresser with tech support system locking out after three 60 min freeze cycles , customer had to keep resetting it . We confirmed hot gas bypass not leaking . Suction pressure never dropped below 55 psi , bad valves , also pulled pump moter to stop water flow should have pulled down a little with no water on evap no suction drop . Bad compressor . Previously adjusted water level to 3/8 inch of of drain pipe to make sure warm water wasn't coming in . Any way change comp . Nine yards ect. Suction now dropping its late seems gravy to 25 psi in freze cycle , I get pulled off for another emergency job I call three hours later the girl says seems like its working I'm thinking I'm golden ! Next morning the girl says she had to restart it again . Any it's still taking 45 to 55 min to make a batch of ice . And locking out after three cycles . Now it seems bottom of evap is making ice top part is thin and week , tried adjusting charge . Tweaking it . I lknow post to weigh it in . But I'm thinking txv not feeding properly head pressure is at 225 at 75• ambient an fan cycle switcher is cycling at 220 cuts out and restarts at 275 and just cyling I tried jumping it thinking that would help but it didn't . Can anyone point me in the right direction , help please

  2. #2
    Join Date
    Dec 2008
    Location
    New York, ny
    Posts
    200
    Check your the evap plate pull a little on them if they loose that's one possibility.

    Sent from my SGH-T999 using Tapatalk 2

  3. #3
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Look for the leak? Sounds like you just lost some charge.

  4. #4

    Yea I think your right

    Quote Originally Posted by Tommy knocker View Post
    Look for the leak? Sounds like you just lost some charge.
    I think your right , I went and recovers charge an only pulled out 4 oz . Dang it I guess you can't skip steps , I might of not put it all back when I recoverd it the first time should have weighed it back in then trying to adjust it after the fact I screwed it all up. Wow look at that with the exact amount of ref 13 0z perfect sheet ice across evap who knew doing it the right way would save you five hours of your life . Lesson to all you hot shots who want to skip the rules ( like me) don't do it :$

  5. #5
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,330
    well done....glad you beat it.....
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  6. #6
    Quote Originally Posted by carmon View Post
    well done....glad you beat it.....
    Thanks for suggestion ,

  7. #7
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    799
    Quote Originally Posted by Daveylouis View Post
    I think your right , I went and recovers charge an only pulled out 4 oz . Dang it I guess you can't skip steps , I might of not put it all back when I recoverd it the first time should have weighed it back in then trying to adjust it after the fact I screwed it all up. Wow look at that with the exact amount of ref 13 0z perfect sheet ice across evap who knew doing it the right way would save you five hours of your life . Lesson to all you hot shots who want to skip the rules ( like me) don't do it :$
    Wait, you recovered a 3/4 lb charge into a standard recovery tank then just put it back without weighing in? I'm surprised it worked at all right after you were done. Your tank, recovery machine and hose residuals can be many ounces. Ice machines are critically charged! When you think about it, if you short it just 1.3 ounces, you are 10% short charged.

    Anytime you are working on a small ice machine like this you should just use virgin refrigerant anytime you have to remove the existing charge. In this case, with a bad compressor, you should have used new for sure.

  8. #8
    Join Date
    Feb 2012
    Location
    So-Cal desert
    Posts
    6

    Atta Boy MicahWes!

    Quote Originally Posted by MicahWes View Post
    Wait, you recovered a 3/4 lb charge into a standard recovery tank then just put it back without weighing in? I'm surprised it worked at all right after you were done. Your tank, recovery machine and hose residuals can be many ounces. Ice machines are critically charged! When you think about it, if you short it just 1.3 ounces, you are 10% short charged.

    Anytime you are working on a small ice machine like this you should just use virgin refrigerant anytime you have to remove the existing charge. In this case, with a bad compressor, you should have used new for sure.
    MicahWes hit it on the head. Anytime you work on a small machine like this undercounter Manitowoc You should use weighed in virgin refrigerant the charge is so critical.

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,855
    Amen.

    I use valves at the end of the hoses, so what I see on the scale is what is IN the ice machine.

    Since I never know who has been there before me, I never re-use what I pull out.

  10. #10
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Quote Originally Posted by timebuilder View Post
    Amen.

    I use valves at the end of the hoses, so what I see on the scale is what is IN the ice machine.

    Since I never know who has been there before me, I never re-use what I pull out.
    Except on warranty repairs rite?

  11. #11
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,855
    Quote Originally Posted by Tommy knocker View Post
    Except on warranty repairs rite?
    Our client has a warehouse of used equipment they have pulled out of sites they have closed, so no, we don't do ANY warranty work.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event