    Gauges for different refrigerants
    what are your beliefs on using the same gauges for different refrigerant systems?
    r-410a with r-22 for example.
    Do you believe it will cause compressor and txv failures?
    Aug 2001
    Pavilion, NY
    Until me and sman met and got married,, I always used separate gauges (22 every day, 22 4way evac, 410 every day, 410 4-way evac) since the honeymoon stage me and ms. Sman share the love with everyone.
    Jul 2009
    Columbia, MD
    may be this should be moved to tools and test equipment?
    I've used my DC (and YJ analogs before that) on various systems containing probably a dozen different refrigerant and at least 4, if not 5 different types of oil.
    As long as good procedures are followed, there isn't a problem.
    Tallahassee, FL
    Yep good techniques are the most important. Me personally has not fallen on the digital bandwagon.
    And I have a Poe set and a mineral set. Basically like the resolution difference.
    Quote Originally Posted by SBKold View Post
    This is the difference.
    If you're using a 410a set on a R134a freezer, you're gonna have problems...
    May 2011
    Western, KY
    Same gauges all the time. I try to do the pull the through technique when removing them(sucking everything through low side) and then I leave the ball valves open so nothing is left in it. I purge the hoses with system pressure every time I hook(I dont work on critically charged systems)
    I've already seen dry r-22 units and replacement compressors using POE so trying to keep gauges dedicated to one type of oil would be hard.
    Tallahassee, FL
    Whys that jp I don't have a problem personally.
    With one division of the gauge being equal to 5 PSIG, it's kind of difficult know what your suction pressure is, exactly, making it more difficult to get an exact superheat.
    Tallahassee, FL
    I see what you mean about that but you will admit the degree difference between 0-5 is negligible.
    Tallahassee, FL
    Actually don't admit that should have looked before. Lol.
    10 degrees is negligible?
    R-134a
    1# = -12.3F
    5# = -3F
    While you can interpolate between gauge lines, even the difference between 1 and 2 psig is nearly 3 degrees.
    Missed that one...