    Fujitsu Minisplit lineset problem

    The residents of our housing complex have 12 Fujitsu Mini Split Ductless Heat Pumps(ASU9RMLQ) that were installed about five years ago. About 25% of the units are non-functioning and a few of the units have run for less than a few hours in that time(some not at all) mostly because of problems that have been associated with the units. Most of the residents are seniors and several are wanting to sell their unit and would like to have the heat pumps functioning for that purpose. We intend on trying to engage a HVAC technician to assist us and to work with us on an ongoing basis but would greatly appreciate some expert advice before we proceed.
    There are a variety of problems associated with these Fujitsu units but the one problem that is common to all the unit is that they were installed with a 1/2 inch suction line rather than a 3/8 inch line as specified by the manufacturer. We attempted on a number of occasions to get some advice from Fujitsu but about all they said was that the warranties on our units are void because of the 1/2 inch line and that we should talk to the installer about it and would not recommend another HVAC technician in our area who would be qualified to work on Fujitsu units. The installer has quit the business. We have had four different HVAC technicians on site at various times and have received conflicting advice with respect to the suction lines. Two have said that the 1/2 inch lines have to be replaced with 3/8 lines at a cost of thousands of dollars per unit and involving significant damage to the walls of about 1/2 the units at least. Other two HVAC technicians said that although the 3/8 inch line would have been preferable the 1/2 line is still acceptable given that the coolant is in a gaseous state in that line. When the compressors are operating the pressures within both lines are well within the parameters specified by the manufacturer and the temperature difference between the in flowing and out flowing air in the wall units where the heat pumps do actually work is about 20F. We realize that operating the units with the 1/2 inch line could affect the life of the units but it is a very temperate coastal climate here and the pumps would only be used for a few weeks in summer and a few hours on the occasional day in winter.
    The decision to install Fujitsu Heat Pumps in our complex has turned out to be most regrettable. Now that we have them, however, we would like to make the best of a bad situation. We would be most appreciative for any advice that may be provided to assist us in putting this problem with the line sets in some sort of perspective.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    5,847
    If the factory says you need 3/8” then what’s the problem.

    The contractor screwed up and:
    a) Doesn’t know mini splits
    b) Didn’t read the install manual
    c) Just didn’t give a ….. took the $ and ran.
    d) All of the above
    You can call as many contractors as you’d like. The large line still has to be changed for proper oil return period.

  3. #3
    Join Date
    Jan 2004
    Location
    Here and there
    Posts
    4,805
    I agree this isnt a Fujitsu issue. If the line sets are wrong . I wonder what else is ........
    i belong to peta ... people eating tasty animals. all my opinions are just mine.

  4. #4
    Join Date
    May 2009
    Location
    Savannah, Ga/H.H. Island, S.C.
    Posts
    1,528
    That particular model Fujitsu mini split is known for having several repair issues.

    But I'm sure the incorrect lineset size doesn't help.

  5. #5
    Join Date
    Sep 2005
    Location
    central jersey
    Posts
    297
    You have to be willing to PAY for an HVAC tech time when dealing with a situation like this. there is no magic bullet. Find someone your comfortable with and allow them to try fixes one unit at a time.

  6. #6

    Thanks for your reply.

    We will be taking that approach. All the HVAC technicians that have been here have been certified and paid for the time they have spent on site.

  7. #7
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,281
    Thread relocated to AOP

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event