02-23-2013, 06:22 AM #14
-
02-23-2013, 04:32 PM #15
Regular Guest
- Join Date
- Feb 2013
- Posts
- 20
Another contractor is suggesting the TT Prestige Excellence PE110 boiler with internal indirect hot water heater. He likes it better than the TT Challenger Combi.
-
02-24-2013, 02:12 AM #16
Regular Guest
- Join Date
- Feb 2013
- Posts
- 20
How do I calculate heat lost base on oil consumption? My energy audit says in 2012 I used 775 gallons of #2 diesel at 79% efficiency. The gov data says that my region had 4753 heating degree days in 2012. I keep the house at 68 degrees. How do I estimate the hourly BTU heat loss from this data?
-
02-24-2013, 04:26 AM #17
18,033.87 BTUs loss per HDD. Multiply that times your highest degree day and then divide by 24.
(BTU content per gallon times Efficiency times gallons used) divided by heating degree days.
EG: 140,000X.79=110,600X775=85,715,000/4753=18,033.87X50(50 is just an example I made up for the highest degree day day)=901,693.5/24=37,570.56 BTU an hour loss.
-
02-24-2013, 05:11 AM #18
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,259
As Beenthere has shown in example, 50 Heating Degree Days is an AVERAGE temperature of 15'F ... 7'F low and 23'F high.
Similarly
Using heat content of 130,000 BTU / gallon for fuel oil.
Use 3,600 hours / 150 days as the heating season
Average temperature is about 33'F ... 4,753 HDD equivalent
22,000 BTU/ hr average will be exceeded about 1/2 the time.
I don't have exact temperature bin data
but to illustrate approximate hours of operation for different outside air temps:
……………… 775 ------------ gallons ………… 4785 HDD
…………. 130,000 ------------ BTU per hr / gallon INPUT ………… 150' Days
……………… 79% ------------ efficiency ………… _______ 31.9' less than 65'
………….. 102,700 ------------ BTU per hr / gallon OUTPUT ………… 33.1' average
…….. 79,592,500 ------------ BTU / year …………
…………….. 150 ------------ Days, 4 -5 months heating season ....... 70 Inside
……………… 24 ------------ hours ………… ....... ........ ..... ... 10 Design
………….. 3600 ------------ total hours in heating season ………… 60 dT
………….. 22,109 ------------ BTU per hr average which is NOT that useful
Outside BTU/HR ----------- Hours % load on furnace BTU used at range
50 ___ 8,000 ------------ 900 __ 0 to 25% ………….. ....... 7,200,000 ... 45000...
36 ___ 17,000 ------------ 1,000 __ 25 TO 50% ………….. 17,000,000 ... 36000
25 ___ 27,000 ------------ 1,070 __ 50 TO 75% ………….. 28,890,000 .... 26750
17 ___ 37,000 ------------ 450 __ 75% TO 90 …………..... 16,650,000 .... 7650
10 ___ 45,000 ------------ 180 __ > 90% ………….. ......... 8,100,000 ,,,, 1800
Avg ___ 21,622 --------- 3,600 __ Total Hours . ………….. 77,840,000 ..117200 __32.56
180 hours at > 90% capacity would be ~ 32 days at 5 or 6 hours each day.
Thanks for the info
Peak heat loss is very likely < 50,000 BTU/HRLast edited by dan sw fl; 02-24-2013 at 05:33 AM.
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
02-24-2013, 05:48 AM #19
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,259
4,665 HDD Groton CT
http://www.wunderground.com/history/...q_statename=NADesigner Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
02-24-2013, 06:01 AM #20Engineering toolbox list #2 oil at 139,600 BTUs.Using heat content of 130,000 BTU / gallon for fuel oil.
-
02-24-2013, 06:02 AM #21
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,259
I see only 27 days < 25'F for low temp.
4,125 HDD Oct 15 2011 - April 12 2012
Differential temperature > 43'F for about 160 hours.
Differential Temp = T-stat setpoint [68] - Outside Air Temp
http://www.wunderground.com/history/...q_statename=NADesigner Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
02-24-2013, 11:54 AM #22
Regular Guest
- Join Date
- Feb 2013
- Posts
- 20
From *removed link to HVAC Forum*
Applying Brad's formula:
BTHU = (Annual Fuel usage/0.6)*(house temp-design temp)*efficiency*fuel heat value)/HDDx24
Where:
68 house temp that we set to
9 design temp from gov data
0.79 efficiency from energy audit
138690 fuel heat value for #2 diesel
775 fuel usage from energy audit/oil company logs
4753 Heating Degree DaysHDD from gov
yields = 73,197 BTU loss per hour
-
02-24-2013, 12:49 PM #23
Professional Member*
- Join Date
- Nov 2011
- Location
- Long Island, NY
- Posts
- 210
The efficiency number from the energy audit is what is skewing the numbers. That is combustion efficiency not system efficiency. At 2000 sq. in Groton, around 40,000 sounds about right. The Slant Fin program works and has a fudge factor included in it.
-
02-24-2013, 01:20 PM #24
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,259
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
02-24-2013, 04:07 PM #25
-
02-24-2013, 04:28 PM #26
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,259
No, but it may very well get one operating times that MANY would Not be real pleased with.
OR a calculated 100,000 * 1.66 ... 166,000 .:. you can have at least 2 units.

Are mechanical contractors now selling 2 for 1 [ BOGO ] like you see in the grocery store?
I'll plan on the _GET ONE_ when my neighbor does the _BUY ONE_ portion.Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities