    Quote Originally Posted by Edgeman View Post
    One contractor is proposing a Navien 175BTU CH-210 Combi with tankless DHW or for $ more a Weil-McLain GV90+5 140BTU mated with an AquaPlus 55 Indirect. I'm think i can scale it back to a Weil-McLain GV90+4 105BTU with an AquaPlau 45 to cut the cost? He suggested the tankless and I suggested a pricing for an indiret instead.
    I have no idea why you would want to over size your boiler so much.

    The Ultra is a better boiler then the GV.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    Join Date
    Feb 2013
    Posts
    20
    Another contractor is suggesting the TT Prestige Excellence PE110 boiler with internal indirect hot water heater. He likes it better than the TT Challenger Combi.

  3. #16
    Join Date
    Feb 2013
    Posts
    20
    How do I calculate heat lost base on oil consumption? My energy audit says in 2012 I used 775 gallons of #2 diesel at 79% efficiency. The gov data says that my region had 4753 heating degree days in 2012. I keep the house at 68 degrees. How do I estimate the hourly BTU heat loss from this data?

  4. #17
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,590
    18,033.87 BTUs loss per HDD. Multiply that times your highest degree day and then divide by 24.

    (BTU content per gallon times Efficiency times gallons used) divided by heating degree days.

    EG: 140,000X.79=110,600X775=85,715,000/4753=18,033.87X50(50 is just an example I made up for the highest degree day day)=901,693.5/24=37,570.56 BTU an hour loss.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #18
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,225
    Quote Originally Posted by Edgeman View Post
    How do I calculate heat lost base on oil consumption? My energy audit says in 2012 I used 775 gallons of #2 diesel at 79% efficiency. The gov data says that my region had 4753 heating degree days in 2012. I keep the house at 68 degrees. How do I estimate the hourly BTU heat loss from this data?
    As Beenthere has shown in example, 50 Heating Degree Days is an AVERAGE temperature of 15'F ... 7'F low and 23'F high.

    Similarly
    Using heat content of 130,000 BTU / gallon for fuel oil.
    Use 3,600 hours / 150 days as the heating season
    Average temperature is about 33'F ... 4,753 HDD equivalent

    22,000 BTU/ hr average will be exceeded about 1/2 the time.

    I don't have exact temperature bin data
    but to illustrate approximate hours of operation for different outside air temps:
    ……………… 775 ------------ gallons ………… 4785 HDD
    …………. 130,000 ------------ BTU per hr / gallon INPUT ………… 150' Days
    ……………… 79% ------------ efficiency ………… _______ 31.9' less than 65'
    ………….. 102,700 ------------ BTU per hr / gallon OUTPUT ………… 33.1' average
    …….. 79,592,500 ------------ BTU / year …………
    …………….. 150 ------------ Days, 4 -5 months heating season ....... 70 Inside
    ……………… 24 ------------ hours ………… ....... ........ ..... ... 10 Design
    ………….. 3600 ------------ total hours in heating season ………… 60 dT
    ………….. 22,109 ------------ BTU per hr average which is NOT that useful
    Outside BTU/HR ----------- Hours % load on furnace BTU used at range
    50 ___ 8,000 ------------ 900 __ 0 to 25% ………….. ....... 7,200,000 ... 45000...
    36 ___ 17,000 ------------ 1,000 __ 25 TO 50% ………….. 17,000,000 ... 36000
    25 ___ 27,000 ------------ 1,070 __ 50 TO 75% ………….. 28,890,000 .... 26750
    17 ___ 37,000 ------------ 450 __ 75% TO 90 …………..... 16,650,000 .... 7650
    10 ___ 45,000 ------------ 180 __ > 90% ………….. ......... 8,100,000 ,,,, 1800
    Avg ___ 21,622 --------- 3,600 __ Total Hours . ………….. 77,840,000 ..117200 __32.56

    180 hours at > 90% capacity would be ~ 32 days at 5 or 6 hours each day.

    Thanks for the info

    Peak heat loss is very likely < 50,000 BTU/HR
    Last edited by dan sw fl; 02-24-2013 at 05:33 AM.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  6. #19
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,225
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  7. #20
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,590
    Using heat content of 130,000 BTU / gallon for fuel oil.
    Engineering toolbox list #2 oil at 139,600 BTUs.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #21
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,225
    I see only 27 days < 25'F for low temp.
    4,125 HDD Oct 15 2011 - April 12 2012

    Differential temperature > 43'F for about 160 hours.

    Differential Temp = T-stat setpoint [68] - Outside Air Temp

    http://www.wunderground.com/history/...q_statename=NA
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  9. #22
    Join Date
    Feb 2013
    Posts
    20
    From *removed link to HVAC Forum*

    Applying Brad's formula:
    BTHU = (Annual Fuel usage/0.6)*(house temp-design temp)*efficiency*fuel heat value)/HDDx24

    Where:

    68 house temp that we set to
    9 design temp from gov data
    0.79 efficiency from energy audit
    138690 fuel heat value for #2 diesel
    775 fuel usage from energy audit/oil company logs
    4753 Heating Degree DaysHDD from gov

    yields = 73,197 BTU loss per hour

  10. #23
    Join Date
    Nov 2011
    Location
    Long Island, NY
    Posts
    280
    The efficiency number from the energy audit is what is skewing the numbers. That is combustion efficiency not system efficiency. At 2000 sq. in Groton, around 40,000 sounds about right. The Slant Fin program works and has a fudge factor included in it.

  11. #24
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,225
    Quote Originally Posted by Edgeman View Post
    From *removed link to HVAC Forum*

    Applying Brad's formula:
    BTHU = (Annual Fuel usage/0.6)*(house temp-design temp)*efficiency*fuel heat value)/HDDx24

    Where:

    68 house temp that we set to
    9 design temp from gov data
    0.79 efficiency from energy audit
    138690 fuel heat value for #2 diesel
    775 fuel usage from energy audit/oil company logs
    4753 Heating Degree DaysHDD from gov

    yields = 73,197 BTU loss per hour
    Annual Fuel Usage / 0.6 ... Now T H A T'S one helluva Fudge Factor !
    1/ 0.6 = 1.6667 ...NOTHING like adding 67% to the Appropriate result _ 43,918 BTU/Hr
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  12. #25
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,590
    Quote Originally Posted by dan sw fl View Post
    Annual Fuel Usage / 0.6 ... Now T H A T'S one helluva Fudge Factor !
    1/ 0.6 = 1.6667 ...NOTHING like adding 67% to the Appropriate result _ 43,918 BTU/Hr
    But it will never under size a unit. ROFL
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  13. #26
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,225
    Quote Originally Posted by beenthere View Post
    But it will never under size a unit. ROFL
    No, but it may very well get one operating times that MANY would Not be real pleased with.

    OR a calculated 100,000 * 1.66 ... 166,000 .:. you can have at least 2 units.

    Are mechanical contractors now selling 2 for 1 [ BOGO ] like you see in the grocery store?
    I'll plan on the _GET ONE_ when my neighbor does the _BUY ONE_ portion.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

Page 2 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event