Thread: Lineset Sizing

  1. #1
    Join Date
    Dec 2001
    Location
    Cartersville Ga
    Posts
    1,035

    Lineset Sizing

    I have a customer looking to replace his 3.5 ton 22 year old Lennox A/C and coil with a 13 SEER system. He currently has a 3/4 X 5/16 line set @ 30' long. I told him we needed to install a 7/8 X 3/8. All other contractors told him he was OK with what he has. Where can I get some information to back me up, or am I wrong here?

    Thanks!
    In the land of the blind the one eyed man is King! semper fi

  2. #2
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    Assuming four long radius 90 bends in the 30' line set, AS/Trane's refrigerant line sizing software recommends 3/4 x 3/8, but 3/4 x 5/16 and 7/8 x 3/8 are both ok too.
    The difference between a 3/4 x 5/16 line set and a 7/8 x 3/8 is a about 430 btuh of capacity, roughly 1%.
    It isn't worth the cost of replacing the lines to get that 1%.

    The smaller lines will potentially result in a more reliable system, due to lower total refrigerant volume, and better oil return.
    If more government is the answer, then it's a really stupid question.

  3. #3
    Join Date
    May 2009
    Location
    Cummins, GA
    Posts
    1,561
    Mark,

    Which Trane software do you use? The engineering toolbox?

  4. #4
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    Quote Originally Posted by Brent Ridley View Post
    Mark,

    Which Trane software do you use? The engineering toolbox?
    The Adtec software.
    It is the software you get if you order the piping software Publication 32-3312-0 listed in the outdoor unit service facts on AS/Trane residential equipment.
    I don't know what the cost of it is now, but a few years ago it was around $160.
    If more government is the answer, then it's a really stupid question.

  5. #5
    Join Date
    Oct 2012
    Location
    Sacramento,ca
    Posts
    198
    Quote Originally Posted by hvac4u View Post
    I have a customer looking to replace his 3.5 ton 22 year old Lennox A/C and coil with a 13 SEER system. He currently has a 3/4 X 5/16 line set @ 30' long. I told him we needed to install a 7/8 X 3/8. All other contractors told him he was OK with what he has. Where can I get some information to back me up, or am I wrong here?

    Thanks!
    Mark is 100% correct. How hard would it be to just replace the 5/16 line only? I have found on many jobs the bigger line isn't worth the trouble but sometimes the liquid line can be changed without to much trouble.

    Mark what does your software say if this were a 15 seer system out of curiosity?

  6. #6
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    Quote Originally Posted by Barrettservices View Post
    Mark what does your software say if this were a 15 seer system out of curiosity?
    SEER is not a variable taken into account in refrigerant pipe sizing.
    If more government is the answer, then it's a really stupid question.

  7. #7
    Join Date
    Jun 2010
    Posts
    168
    With running 5/16th on the liquid line instead of 3/8th there will be a higher head pressure. By under sizing the liquid line you would think the extended head pressure would hurt a compressor some.

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,763
    Quote Originally Posted by mark beiser View Post
    Assuming four long radius 90 bends in the 30' line set, AS/Trane's refrigerant line sizing software recommends 3/4 x 3/8, but 3/4 x 5/16 and 7/8 x 3/8 are both ok too.
    The difference between a 3/4 x 5/16 line set and a 7/8 x 3/8 is a about 430 btuh of capacity, roughly 1%.
    It isn't worth the cost of replacing the lines to get that 1%.

    The smaller lines will potentially result in a more reliable system, due to lower total refrigerant volume, and better oil return.
    Need to know if the indoor is higher then the condenser, and if so by how much.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Dec 2001
    Location
    Cartersville Ga
    Posts
    1,035

    Good info!

    Quote Originally Posted by Baycienda View Post
    With running 5/16th on the liquid line instead of 3/8th there will be a higher head pressure. By under sizing the liquid line you would think the extended head pressure would hurt a compressor some.
    this is a ranch on a slab, lineset @ 30', coil 12' above compressor


    Thank you for your input. I have leaned something here
    In the land of the blind the one eyed man is King! semper fi

  10. #10
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,503
    I'm surprised the R410a system requires larger lines than a R22 system.

  11. #11
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    Quote Originally Posted by 54regcab View Post
    I'm surprised the R410a system requires larger lines than a R22 system.
    It doesn't.
    If more government is the answer, then it's a really stupid question.

  12. #12
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,503
    Quote Originally Posted by mark beiser View Post
    It doesn't.
    Is it the 13 SEER that's requiring the larger lineset?

  13. #13
    Join Date
    Oct 2012
    Location
    Sacramento,ca
    Posts
    198
    Quote Originally Posted by 54regcab View Post
    Is it the 13 SEER that's requiring the larger lineset?
    I just had a rheem 3-ton 13 seer 410a install today that spec. 7/8" @ the condenser but the same 3ton 15 seer only spec 3/4" @ condenser. why is this?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event