    COLEMAN trailer trash...,

    Mod DGAA070 BDTA..,Ser. 031002087 Guys.,dont work on these furnaces normally. Intermintant start up issue.,arrived #3code.,stuck pressure switch.checked the usual,hoses,elec,.Then it started ran few time then got #2code open P/Sw. Decided to check inducer motor pressure..,Where is it! of course its in the 4inch intake pipe, took readings, its a 2 hose P/Sw got 0 on one .04inwc on other. Iguess my question is..,how much will this "watch" motor pull?..,how do you get things apart to replace it (has closed Combustion) thing would not act up again while I was there.,I at least want to replace P/S since I believe i found it "stuck' twice! Any thoughts..,thanks ahead. P/Sw.rating was 0.18pr.

  2. #2
    Join Date
    Aug 2012
    Location
    NE wisconsin
    Posts
    402
    Looks to be 10 years old, I would go on the roof and take a close look at the inside of the roof jack they like to rust from the inside out. The inducer doesn't pull much vacuum not sure on a number usually if its above the switch rating its fine. To get the inducer out pull the front off the combustion chamber and it falls right out.

  3. #3
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    5,594
    Quote Originally Posted by Cosmicmuffin View Post
    Mod DGAA070 BDTA..,Ser. 031002087 Guys.,dont work on these furnaces normally. Intermintant start up issue.,arrived #3code.,stuck pressure switch.checked the usual,hoses,elec,.Then it started ran few time then got #2code open P/Sw. Decided to check inducer motor pressure..,Where is it! of course its in the 4inch intake pipe, took readings, its a 2 hose P/Sw got 0 on one .04inwc on other. Iguess my question is..,how much will this "watch" motor pull?..,how do you get things apart to replace it (has closed Combustion) thing would not act up again while I was there.,I at least want to replace P/S since I believe i found it "stuck' twice! Any thoughts..,thanks ahead. P/Sw.rating was 0.18pr.
    The draft proving switch activates at 0.20 inches of air pressure.

    The pressure switch is normally open. The suction pressure from the intake side, and the positive pressure from the output side, both add up to a positive pressure on the diaphragm of the pressure switch, which causes the electrical contacts inside the pressure switch to close completing the circuit to the IFC.

    Send me an emil (address is in my profile), and I will get a service manual off to you on this unit. I don't post manuals in this "OPEN" Tech-Tech forum.
    Instead of learning the tricks of the trade, learn the trade.

  4. #4
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    2,013
    Call to mobile home in winter in snow country = make sure you have your long ladder with you. When you drive up, make sure the first thing you do before going into the house is locate the chimney assembly and see if it's buried in a snow drift. IMO
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  5. #5
    Join Date
    Aug 2012
    Posts
    2,663
    Those are not that hard to change out they come inside their own pipe assembly, you just slide it out and reassemble off you go.
    My name is TooCoolforschool and I am a chronic over charger.

  6. #6
    Join Date
    Jun 2004
    Location
    Howell, Michigan
    Posts
    16,176
    They have major pressure switch issues, the switch actually closes but the resistance across the contacts is too much for them to actually complete the circuit.

    There is also an updated switch available, for more than a year or so. We should have this moved into "Pro" and then maybe we can share more info like part numbers etc.

  7. #7
    Join Date
    Dec 2011
    Location
    Twin Cities Minnesota
    Posts
    239
    Picked up new pressure switch,rated .10 pr old one was .18pr. Been 48hrs no call backs! Thanks all for your input.,rundawg.,you the man!

  8. #8
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    1,815
    If I read your post correctly you replaced the pressure switch with one with a different, lower rating. I would have reservations about improper venting but the switch would still close instead of performing its function as a safety device.

  9. #9
    Join Date
    Feb 2013
    Location
    Champaign, IL
    Posts
    42
    Quote Originally Posted by Cosmicmuffin View Post
    Picked up new pressure switch,rated .10 pr old one was .18pr. Been 48hrs no call backs! Thanks all for your input.,rundawg.,you the man!
    Unless this was a supercede, that was most likely NOT a good idea....

  10. #10
    Join Date
    Feb 2013
    Location
    north georiga
    Posts
    598
    its been a few years, but i was told by the factory that there is a "diverter" plate at the top of the heat exchanger where the flue connects, it's purpose was to slow the combustion gas to improve it's efficiency rating, but it tends to catch carbon and restrict the flue. i was told to remove the flue cap and give it a light tap with a stick. it mostly happens on l.p. units.

  11. #11
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    3,425
    Quote Originally Posted by Cosmicmuffin View Post
    Picked up new pressure switch,rated .10 pr old one was .18pr. Been 48hrs no call backs! Thanks all for your input.,rundawg.,you the man!
    Uh...I would give some more, serious thought to this solution. If the manufacturer specified .18 or better, that's what that furnace needs to safely vent. You have exposed yourself to a huge liability.

  12. #12
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    517
    Quote Originally Posted by hurtinhvac View Post
    Uh...I would give some more, serious thought to this solution. If the manufacturer specified .18 or better, that's what that furnace needs to safely vent. You have exposed yourself to a huge liability.
    Don't worry about it. Those were superceded to the new .10" rating months ago. Some of the old ones were .18" some were .15" they all get a .10" now.

  13. #13
    Join Date
    Feb 2013
    Location
    Sonora, California, United States
    Posts
    1,022
    [QUOTE=HeyBob;15260441]They have major pressure switch issues, the switch actually closes but the resistance across the contacts is too much for them to actually complete the circuit.

    this just cleared up some of my recent confusion.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event