    Restriction from hell

    I love a good challenge and the chance to learn something new. But this one was ridiculous.

    With the correct charge weighed in the suction would pull into a vacuum after about 30 seconds and the head pressure would run about 270 psi.

    Now this is a new house. First time the A/C has been run.

    After over charging the system enough to get some suction pressure returning to the unit I was able to check the line temperatures inside and out. Only the usual 2-3 degree temperature difference. By this time the pressures were 650/125. So I did not let it run very long like that. Replaced the TXV at the indoor coil. While it was apart I blew through the line set with plenty of nitrogen. no problems. Put it back together....Same problem.... Next I ran a temporary new liquid line down the attic access hole and out a window to the outdoor unit....Same thing... By this time I'm getting pretty frustrated. Finally I pulled the evaporator and brought it outside. Sat it on top of the condenser and piped it in. Finally it worked. Now came the hard part. Replacing a 90 foot line set in a fully finished $500,000 house.

    After all day the new line set fixed the problem. How ever I was never able to locate a problem with the line set I pulled out.

    Just a side note. The line set I pulled out was aluminum.

  2. #2
    Join Date
    Nov 2004
    Location
    South Carolina
    Posts
    1,864
    Post Likes
    aluminum?????????????????????????
    It is what it is unless I say differently !!!!

  3. #3
    Join Date
    Jan 2013
    Location
    Frederick, MD
    Posts
    52
    Post Likes
    Thread Starter
    Yes Aluminum. My company gave it try. It was in an effort to cut cost. They have since changed their minds and we no longer use it.

  4. #4
    Join Date
    Nov 2004
    Location
    South Carolina
    Posts
    1,864
    Post Likes
    sorry never heard of it in residential work
    It is what it is unless I say differently !!!!

  5. #5
    Join Date
    Jan 2013
    Location
    Frederick, MD
    Posts
    52
    Post Likes
    Thread Starter
    Name:  photo.JPG
Views: 442
Size:  135.7 KB

  6. #6
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    someone forgot to take the plug out the lineset, or the coil

  7. #7
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Quote Originally Posted by Frederick_Tech View Post
    Yes Aluminum. My company gave it try. It was in an effort to cut cost. They have since changed their minds and we no longer use it.
    Probably cost them >100x what they were trying to save on that job, lol.

  8. #8
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Who sells aluminum line sets ?

  9. #9
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Was there a kink in it somewhere, I can see where aluminum would be easy to kink.

  10. #10
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,905
    Post Likes
    How do you connect and aluminum line set? Can you braze it?

  11. #11
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,430
    Post Likes
    Also, I would be interested in the method used to seal the connections at the coils(what material was the aluminum joined to at coils) and the splice since it was 90'.

  12. #12
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Did it have a copper coated stubs on the ends? Not too uncommon to have copper coated steel on bigger stuff....

  13. #13
    Join Date
    Apr 2013
    Posts
    11
    Post Likes
    Was the replacement line set the same size? Also was the length and lift of the line set within specifications? I'm not seeing how the line set was a problem no matter the material if it had good flow through it with nitrogen. That's why I'm wondering if any sizing or routing was done differently with the line set. 90 feet is a good haul and units like trane 20i's are real funny about that length and lift

  14. #14
    Join Date
    Aug 2012
    Location
    Antelope,Ca
    Posts
    93
    Post Likes
    Quote Originally Posted by papa_jo View Post
    aluminum?????????????????????????
    from what i heard, a company in my area also installed a housing tract with that stuff. i personaly have not ran accrosed it! Yet

  15. #15
    Join Date
    Jan 2013
    Location
    Frederick, MD
    Posts
    52
    Post Likes
    Thread Starter
    Not sure where the stuff is purchased from. We use a solider that can join aluminum to aluminum, copper, or brass. Below is a link to a demonstration video.

    http://youtu.be/AiZKl0nvglk

  16. #16
    Join Date
    Jan 2013
    Location
    Frederick, MD
    Posts
    52
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    Was there a kink in it somewhere, I can see where aluminum would be easy to kink.
    I checked ever inch of the line set. No kinks at all.

  17. #17
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    I had to use some aluminum solder to fix a leak in a microchannel coil. Had to pull a vacuum while soldering to suck the material into the hole.

  18. #18
    Join Date
    Jan 2013
    Location
    Frederick, MD
    Posts
    52
    Post Likes
    Thread Starter
    Quote Originally Posted by Munkywrench View Post
    Was the replacement line set the same size? Also was the length and lift of the line set within specifications? I'm not seeing how the line set was a problem no matter the material if it had good flow through it with nitrogen. That's why I'm wondering if any sizing or routing was done differently with the line set. 90 feet is a good haul and units like trane 20i's are real funny about that length and lift
    Its on a Carrier 2 ton condenser. The line set is 3/4 suction and 3/8 liquid. I went back in with the same size. Even took the exact same rout through the house. Only took 32 holes in the drywall. That is why I saved that as a last option.

  19. #19
    Join Date
    Jan 2013
    Location
    Frederick, MD
    Posts
    52
    Post Likes
    Thread Starter
    Quote Originally Posted by gravity View Post
    someone forgot to take the plug out the lineset, or the coil
    Well I didn't find the plug inside the line set but all I can figure is something must have been loose floating around inside it. I cut the lines into 2 foot sections after I pulled it out and still never found anything. This does not mean it didn't fall out during the process of removing it from the house.

  20. #20
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,430
    Post Likes
    Quote Originally Posted by Frederick_Tech View Post
    Not sure where the stuff is purchased from. We use a solider that can join aluminum to aluminum, copper, or brass. Below is a link to a demonstration video.

    http://youtu.be/AiZKl0nvglk
    Wow! I'm hoping you're not citing this video for it's instructional value.

    If that's how your line was done then my guess is there was a 1/4 roll of solder moving through the lines or just plugging up at one of the joints because it didn't break off the inner wall.

    BTW, not trying to bash you or anyone else, it's just that the guys in the video appear to lack experience and it could mislead others that want to learn how to solder correctly.
    Last edited by mason; 04-28-2013 at 05:00 PM.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •