    dual heat system - can it be set to heat with gas only?

    Hi

    I have a source 1 gas furnace and a heat pump. Currently, where i live, electricity is significantly more expensive than gas. The controller can be set so that I can choose electric heat only, but there is no option for gas heat only. The temperature in the winter time here is often between 0 and 5 degree celcius so often the heat pump will run for heating, but it will run for a long time and it is not that hot. then when it gets a little colder, the gas kicks in and it heats the place in a few minutes.

    So, in the current set up, the heat pump is running for a long time and the electrical bill is going through the roof.

    Is there a controller change that I can have done or is it a software change?

    please help

    thanks

    bruce

  2. #2
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,520
    A dual fuel thermostat with Assn outdoor sensor would let you lock it out based on outdoor temp. Set the lo temp to 55f

    Sent from my DROID RAZR using Tapatalk 2

  3. #3

    controller

    Could the controller that is already in place have the option of changing the points when it switchs from heat pump to gas? Is there a way I could determine this?

  4. #4
    Join Date
    May 2006
    Location
    Austin, Texas
    Posts
    298
    Does thermostat have an emergency heat setting. Our controls are set for gas only by selecting em heat. Just a simple thought.

  5. #5
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,035
    What thermostat do you have?
    Beware of advice given by some guy on the Internet.

  6. #6
    Hi

    I got the manual out tonight and read it in detail and it explained how to change the balance points. So I increased the low balance point a couple of degrees and it is now running on gas when the temperature is a little above zero.
    Thanks all for the responses.

  7. #7
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,520
    Your balance points usually get set for fuel costs. But 0C (32F) is abotu where most end up given typical fuel costs and equipment effciency. IF electric rates are high it might be clsoer to 40F, if electric is cheap, if might be down around 25F. The thermal balance point where the heat pump can;t keep up, if sized for cooling load, in northern climate will usually be aroung 35-40F. IN a southern climate, it might be 20F.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event