    over sized hot water heater flue

    Installed a new 90% furnace and vented out the side wall. The hot water heater is still vented in to the 6 b-vent flue. Has anyone had a problem when doing this?

  2. #2
    Join Date
    Jun 2009
    Location
    Alberta, Canada
    Posts
    1,093
    Post Likes
    it could have problem with condensation and possibly down draft/spillage... you might be able to fit 4 inch liner down the hole. you need to do your venting calculation.
    Have tools and gauges, will travel.
    ------------------------------------------------------


    RIDGID|YELLOW JACKET|UEI|TESTO|STANLEY|CPS|VETO| KLEIN|MILWAUKEE|MASTERCRAFT|

  3. #3
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,155
    Post Likes
    You are allowed x7 the cross-sectional area by code but combustion analysis will tell you if it is working or not.

  4. #4
    Join Date
    Jun 2012
    Location
    Ontario
    Posts
    6
    Post Likes
    Condensation will be the main issue. Also depending where you are, but here in Ont, you can only go one size larger on a forced device then the flue collar size. so if you're a 4" flue collar you'd have to change the size to 5" to be in code.Blitz nailed it. vent size calculation chart

  5. #5
    Join Date
    Dec 2008
    Posts
    52
    Post Likes
    I know this sounds petty, but in our trade, it is a "water heater" not a hot water heater. 6 inch b-vent should be fine, depending on the vertical height. In some areas, because of the vertical height of the main stack, when you orphan a water heater, the connector pipe must be b-vent, to keep the flue gas temperatures up enough before they get to the 6 inch stack. In our area, which is WSSC territory in Maryland, if you touch the flue pipe for a furnace install, you own the entire furnace and water heater flue piping, even if the water is 20 years old. It is up to you, to bring everything up to current code.