    2000ppm in cellar..feeling woozy..RUN!

    Crappy rental property, owner calls stating maintenance is tired of re-lighting pilot light of furnace. Showed up and meet tenants and was taken back to an old cellar in the back of the home. No door just cement steps down into the dark. Waiting for my eyes to adjust to get my bearings I started to see green spots and felt woozy.
    Been through CO and combustion training and have almost been wiped off the face of the earth years prior in a boiler room with large amounts of CO, that my spider senses triggered and I was out of that cellar.
    Shut the gas off at the meter and grabbed my dedicated CO monitor. It has the verbal option which blurts out the ppm every minute or so. This has become my buddy in old boiler rooms hanging on the wall while I work.
    At the door I get 30ppm, tape the end to a 10ft piece of PVC laying on the ground and insert it in the cellar and my buddy is chatting back from the darkness...2020ppm.
    Tenant had a fan, held my breath and placed it at the base of steps and left it running for a few hours. In the home I was only getting about 20ppm in the bedrooms, but 70ppm in the kitchen closest to cellar....told tenants to leave until things settled down. THANK GOD, cellar is not directly under home, cellar door was broken and left open and what little flooring near this cellar was the kitchen with three layers of laminate, the place they married the cellar to the home, they busted through to the 1 foot crawler to run a few flex runs, this was ventilated or these tenants wouldn't be around.

    Here is what I finally found when it was safe to enter.

    1) New water heater was installed a week prior by this maintenance guy. Too tall, so maintenance guy dumped the diverter and just placed the flue pipe directly on top.
    2) Old Lennox G12 must have been found somewhere, scrapped, and thrown in 4 inch flue dropped into the manufacturer 6 inch and taped off. All the exchangers sooted near closed...
    3) Panels long gone, sheet metal used as blower door
    Could go on and on.

    Another rental property disaster diverted...so happy 99% of my stuff is commercial. Figure fate would have it that I was asked to look at this job instead of one of our newbies...don't think they would have had the experience to know CO poisoning, and tragedy could have happened.Our company replaced the furnace, water heater, and landlord learned a valuable lesson about cheap maintenance guys.
    Attached Images Attached Images    

  2. #2
    Join Date
    Jan 2009
    Location
    Salisbury, Maryland
    Posts
    156
    Post Likes
    Wow, speechless..........

  3. #3
    Join Date
    Aug 2012
    Location
    NE wisconsin
    Posts
    488
    Post Likes
    Glad your still with us.

  4. #4
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    so.....where is all the CO coming from?

  5. #5
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    have a "eddy" current from high of draft which is causing spillage at the draft diverter on furnace?

    or is the flue clogged and it's spilling out the draft diverter of the furnace?

    or is the sheet metal blower door causing a negative in CAZ ?

  6. #6
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    Thread Starter
    Quote Originally Posted by gravity View Post
    have a "eddy" current from high of draft which is causing spillage at the draft diverter on furnace?

    or is the flue clogged and it's spilling out the draft diverter of the furnace?

    or is the sheet metal blower door causing a negative in CAZ ?
    You name it....didn't care to figure out exact cause. Severely sooted exchangers and diverter...so assume furnace. Just shut off gas, called owner and next day they gutted and replaced everything.

  7. #7
    Join Date
    Jul 2007
    Location
    Chicago IL
    Posts
    167
    Post Likes
    Frickin' criminal. That was close to being a news story.
    I'm guessing the combustion was spilling? Like Gravity I'm curious where the co was coming from.

  8. #8
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    I would want to figure out what caused it to soot.

    It is really hard to soot up a NG unit.

  9. #9
    Join Date
    Aug 2012
    Location
    NE wisconsin
    Posts
    488
    Post Likes
    Maybe that fancy 6-4 reducer, the nice venting on that water heater probably tees in with the furnace vent, that and years of neglect.

  10. #10
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    Thread Starter
    Sometimes in these cases, the saying "curiosity kills the cat", could apply hear. CO was there and at deadly levels, not about to turn on gas, relight appliances, and dink around. One look at the equipment, installation, flue, and every other thing was enough for me to call "time-out", call in the troops, and get rid of this entire monstrosity.

    If I had to speculate:

    I believe the furnace was involved in a flood in it's prior life, there is a water line on furnace, with rusting, hard to explain but you all know what I mean. It was removed to be scrapped and some how some way ended up here. I believe those ribbon burners and cross-overs were probably clogged to the hilt and back. Signs of severe roll-out...thus the pilot always going out. On top of this the dirty burners probably were generating a real crappy mix ratio and causing sooting. Sooting is like a snow fall, just builds in layers and finally over time slowly restricts the heat exchangers. The restricted path for the vent gases, plus the improper flue, with what I assume minimal draft, lead to a good percentage of the high CO level vent gases to dump into the cellar.
    My opinion, and I think a pretty educated one at that.

  11. #11
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    929
    Post Likes
    I agree, who cares what was causing it? Its enough to know co was high and that there was multiple possible causes. Just rip it out and bring it all to code.

  12. #12
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Good thing you got out of there alive!

    This is why I don't go anywhere without a CO monitor clipped to my belt. It is a rare day where it doesn't show at least 15 ppm.

  13. #13
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Yikes. Did the people living there go buy a lottery ticket after this?

  14. #14
    Join Date
    Jan 2013
    Location
    Henry county,ky
    Posts
    82
    Post Likes
    just glad to see its not this.


    I know about the boilers rooms, had a near death co experience myself. Where did you get the co buddy. I would like to get one of those myself. Landlords kill me, they think they are getting a deal because something is cheap. He's lucky no died and took him to court. That's just uncalled for

  15. #15
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    At what ppm do you go to sleep at?

  16. #16
    Join Date
    Aug 2012
    Location
    Antelope,Ca
    Posts
    93
    Post Likes
    6400 ppm death in 15 min, 12800 ppm death in 3 min

  17. #17
    Join Date
    Mar 2009
    Location
    Winnipeg, Manitoba, Canada
    Posts
    17
    Post Likes

    Co

    Quote Originally Posted by gravity View Post
    so.....where is all the CO coming from?
    Lack of combustion air, improper flue collar on a nat draft appliance, and the fact that these units prolly have never been looked at by someone qualified.
    Glad to hear it didn't KO you!

  18. #18
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by ryan1088 View Post
    At what ppm do you go to sleep at?
    At 2,000 ppm a healthy adult would be unconcious at around 15 minutes.

  19. #19
    Join Date
    Jun 2012
    Posts
    530
    Post Likes
    Quote Originally Posted by gravity View Post
    I would want to figure out what caused it to soot.

    It is really hard to soot up a NG unit.
    It's not really hard. It doesn't always take long. Like another poster said it snowballs. Once it starts sooting if conditions are not corrected it starts piling up in the HX. Once it starts layering it makes the A/F ratio even worse producing more and more soot until it's noticed/fails.

  20. #20
    Join Date
    Jul 2007
    Location
    Chicago IL
    Posts
    167
    Post Likes
    "who cares what was causing it?"

    The OP probably saw enough of the furnace to have confidence of the source and knew it was the right call. I still like knowing if my license is on the line. Swapping put the furnace obviously isn't enough if the issue is a restricted chimney or malfunctioning water heater. Squirrels are good at getting in 3" rounds here. It only takes a few minutes to isolate equipment.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •