Thread: Iced up Coil.

  1. #1
    Join Date
    Feb 2011
    Location
    Philadelphia PA
    Posts
    4

    Iced up Coil.

    I went to a two door freezer and found the coil iced up. Forced the unit on defrost and realized that the relay that energizes the electric heaters was not closing the contacts. Replaced the relay and checked the unit defrost and refrigeration mode, all ok. Is there anything else I shoild have checked? Don't feel confident I solved the problem

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,575
    Model and serial #? How did you determine the relay was bad?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  3. #3
    Join Date
    Feb 2011
    Location
    Philadelphia PA
    Posts
    4
    Yes the relay was bad. Mo is GDM-49F

  4. #4
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,575
    Relay on the Grasslin timer?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  5. #5
    Join Date
    Dec 2012
    Location
    Spokane, Washington
    Posts
    124
    If you see Kay...tell her that GDM freezer is iced up again!
    A smooth sea has never made a worthy mariner
    English proverb

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event