Results 1 to 13 of 22
Thread: Lineset Sizing
    Dec 2001
    Woodstock Ga
    Lineset Sizing
    I have a customer looking to replace his 3.5 ton 22 year old Lennox A/C and coil with a 13 SEER system. He currently has a 3/4 X 5/16 line set @ 30' long. I told him we needed to install a 7/8 X 3/8. All other contractors told him he was OK with what he has. Where can I get some information to back me up, or am I wrong here?
    Thanks!
    In the land of the blind the one eyed man is King! semper fi
    Assuming four long radius 90 bends in the 30' line set, AS/Trane's refrigerant line sizing software recommends 3/4 x 3/8, but 3/4 x 5/16 and 7/8 x 3/8 are both ok too.
    The difference between a 3/4 x 5/16 line set and a 7/8 x 3/8 is a about 430 btuh of capacity, roughly 1%.
    It isn't worth the cost of replacing the lines to get that 1%.
    The smaller lines will potentially result in a more reliable system, due to lower total refrigerant volume, and better oil return.
    May 2009
    Cumming, GA
    Mark,
    Which Trane software do you use? The engineering toolbox?
    Quote Originally Posted by Brent Ridley View Post
    Mark,
    The Adtec software.
    It is the software you get if you order the piping software Publication 32-3312-0 listed in the outdoor unit service facts on AS/Trane residential equipment.
    I don't know what the cost of it is now, but a few years ago it was around $160.
    Oct 2012
    Sacramento,ca
    Quote Originally Posted by hvac4u View Post
    Thanks!
    Mark is 100% correct. How hard would it be to just replace the 5/16 line only? I have found on many jobs the bigger line isn't worth the trouble but sometimes the liquid line can be changed without to much trouble.
    Mark what does your software say if this were a 15 seer system out of curiosity?
    Quote Originally Posted by Barrettservices View Post
    SEER is not a variable taken into account in refrigerant pipe sizing.
    Jun 2010
    With running 5/16th on the liquid line instead of 3/8th there will be a higher head pressure. By under sizing the liquid line you would think the extended head pressure would hurt a compressor some.
    Need to know if the indoor is higher then the condenser, and if so by how much.
    Dec 2001
    Woodstock Ga
    Good info!
    Quote Originally Posted by Baycienda View Post
    this is a ranch on a slab, lineset @ 30', coil 12' above compressor
    Thank you for your input. I have leaned something here
    Jun 2001
    I'm surprised the R410a system requires larger lines than a R22 system.
    Quote Originally Posted by 54regcab View Post
    It doesn't.
    Jun 2001
    It doesn't.
    Is it the 13 SEER that's requiring the larger lineset?
    Oct 2012
    Sacramento,ca
    I just had a rheem 3-ton 13 seer 410a install today that spec. 7/8" @ the condenser but the same 3ton 15 seer only spec 3/4" @ condenser. why is this?